Hydraulic balancing air-water heat pump + efficiency circulation pump

  • Erstellt am 2021-01-03 23:07:06

lesmue79

2021-01-05 10:25:53
  • #1
Sorry I couldn't edit the previous post anymore:

I also have the feeling that the temperatures in the house are rising faster?
 

T_im_Norden

2021-01-05 11:12:16
  • #2
Do not adjust anything yet. The tendency is that the temperature is still rising, and the outside temperature is lower.

What does tilting the window mean in terms of time?

Briefly for 5 minutes or tilt permanently? With a permanent tilt position, of course you are heating outside as well, and your entire heating load calculation is no longer accurate because the heat loss to the outside is greater.

It may be that the underfloor heating feels like it reacts differently because the flow rate and thus the heat output is probably faster.

How was the consumption?
 

T_im_Norden

2021-01-05 11:20:10
  • #3
In your table, you can clearly see why equal pipe lengths are better for underfloor heating.

All those that have approximately the same length also have the same flow rate.
 

lesmue79

2021-01-05 11:58:13
  • #4
I'm currently out of the house and won't be home for another hour...

I can only give you the consumption figures tonight because the 24 hours will only be complete then... I only discovered the menu item for it last night.

The windows are not permanently tilted but certainly for half an hour or an hour, for example, when cooking or airing out in the morning.
 

lesmue79

2021-01-05 15:30:04
  • #5
Currently, thanks to a slightly increased outside temperature, the supply setpoint was also slightly exceeded by the actual supply, and the energy integral has begun to decrease.
 

lesmue79

2021-01-05 18:16:38
  • #6
So, attached are the consumption figures from yesterday to today:

Energy generated by heat pump
for heating and hot water = 84 kWh

Energy consumed for it
for heating and hot water = 20 kWh

84/20 = COP of 4.2
 

Similar topics
13.06.2012Underfloor heating and mechanical ventilation with heat recovery (MVHR), replacement of ordinary radiators23
09.12.2012Climate blanket vs. underfloor heating13
23.08.2013Electric heating, underfloor heating, gas condensing technology instead of radiators?10
04.11.2013Underfloor heating, room thermostats and cold tiles28
20.12.2013New underfloor heating instead of radiators and controlled residential ventilation; yes or no?15
24.02.2014KFW55 house with underfloor heating... which type of flooring?11
28.01.2016Why are modern houses so warm?32
12.11.2017Underfloor heating / Wall heating / Ceiling heating - Alternatives?18
25.11.2017Underfloor heating is not getting warm - 20,000 kWh consumption11
13.07.2019It takes a long time for hot water to come27
01.11.2019Extremely high heating costs with underfloor heating. Incorrect setting?13
12.11.2021Central room temperature controller for ERR underfloor heating76
10.08.2020How to tell if underfloor heating is running - ERR still without thermostat cover50
04.01.2022Air-water heat pump current consumption and data1439
15.12.2022Electricity consumption at home, what is your consumption?418
14.12.2020Underfloor heating heat load calculation - simply explained?26
10.04.2022Solid wood parquet on underfloor heating101
03.01.2022Geothermal heat pump single-family house 200m² underfloor heating kfw55 - setting/optimization91
31.03.2023Is the Vitodens 200-W sufficient for underfloor heating?17
21.11.2024Underfloor heating on the upper floor - one room always remains too cold20

Oben