is (unfortunately) right in practice. Especially if you don’t take care of it in time..
For a well and efficiently running heat pump, due to the lack of motivation and knowledge of most heating engineers, self-initiative is required.
That means:
Have a proper heating load calculation done.
Have the underfloor heating designed according to the heating load calculation with a maximum flow temperature of 32 degrees Celsius.
Probably use wall heating in the bathrooms.
Matching heating circuits with about 80 meters per circuit.
Omitting buffer storage and bypass valve.
Adjustment and balancing of the system in the first winter.
It often already fails at the heating load calculation, because the experienced heating engineer still estimates. This results in massively oversized units being installed.
The calculation of the underfloor heating is the same. Nobody wants to invest time there.
In addition, heating engineers often add a large markup on the heat pump price during the sale. Which makes the heat pump particularly unattractive.
If you consider the above points, you get a heating system with which you never have to adjust anything again after the first winter and which is extremely low-maintenance. This keeps the follow-up costs very manageable. As long as you don’t have a fireplace, you will never see the chimney sweep again, can save the basic gas fee and the connection fee as well.
Replacing the heat pump in many years is also very easy to manage. A few cables and two pipes.
However, the system from does not seem to run really well despite all optimization. Apart from that, providing hot water via solar is not free, because the solar thermal system had to be purchased and installed.
Conclusion: I am an interested layperson and would pay attention to the above-mentioned requirements anyway in order to remain flexible in the future.
For me, only a heat pump in a new building would be an option.
Gas is simpler. The heating engineer’s planning errors do not matter as much on the operating cost side.