gumel81
2020-05-21 11:56:40
- #1
Which annual performance factor did you calculate with which supply temperature? I suspect it will depend on the supply temperature and your general contractor thinks that due to the size he has to increase the supply temperature and thus the calculated annual performance factor drops below 4.5.
I used the annual performance factor calculator on Tecpalor. The maximum supply temperature is set to 35 degrees by default in the calculator. The calculator then outputs an annual performance factor of 4.57 for the Tecpalor 5.5 Eco. I did not change any other values.
Have your heating load calculated according to DIN first, it will very likely be below 5 kW. Or do you live in Siberian climate? What is the standard outdoor temperature?
In my calculator the standard outdoor temperature is -14 degrees. No, I don't live there... southern Germany.
Especially with KfW40 you will hardly find a BAFA-eligible air-to-water heat pump that is small enough for your actual heating load. So you will have to oversize somewhat.
The Tecalor has the following values:
Heating capacity at A-7/W35 (EN 14511) 5.5 kW
Heating capacity at A2/W35 (EN 14511) 5.16 kW
Heating capacity at A7/W35 (EN 14511) 4.4 kW
Do these values have to match the heating load?
What do you mean by oversizing? An air-to-water heat pump with higher heating capacity values?