driver55
2021-06-02 11:16:51
- #1
By "heat pump does not run in D" I meant, who on earth is cooling now when most have just turned OFF their heating about 4 weeks ago.
The temperature increase of the source is normal when idle.
Regarding your observations/ measurements. Something is off. If the heat pump runs for over 60 minutes, the source temperature (outlet) can never rise! With an ideal brine pump setting, the temperatures basically drop in sync. Delta approx. 3 K.
A warm water temperature increase of just 7 K in 60 minutes is not normal. It should be much faster. (Unless it might be about 1000 l).
Have you ever read the heating capacity of the heat pump? With how many kW does it "push" into the storage? (According to the datasheet and what you read!)