MayrCh
2022-11-09 07:33:53
- #1
The temperature difference that is measured is the delta between supply and return. This delta can be measured before the heat exchanger, i.e., on the network side, but also after the heat exchanger, i.e., on the customer side. The latter would also be correct in my opinion if the [WT] belongs to the network operator. If measured after the [WT], the losses of the [WT] do not appear in your energy balance and thus in the heat consumption.