This is the wrong section. I have looked up the three relevant levels for you. Moisture protection is the ventilation you need when you are on vacation. You have to look at rated ventilation, which is for everyday life with people in the house, cooking, showering, and so on. And I can promise you that there will be much more than 0.1 air changes per hour.
The core element of the DIN 1946-6 standard is the distinction of four ventilation levels of different intensities, which we present to you here in more detail:
Ventilation for moisture protection (FL)
This ventilation level is intended to achieve adequate ventilation of the building depending on the respective thermal insulation level. The aim is to avoid building damage due to moisture even when the occupants of the room are temporarily absent and the moisture loads are reduced, for example, because drying laundry is consciously avoided. This means: A correspondingly designed ventilation must therefore operate independently of the user.
Reduced ventilation (return flow)
This ventilation level must also be largely independent of the user. It must be ensured that even when the occupants are only absent for a short time due to, for example, their job, the ventilation meets hygienic minimum standards and building protection.
Rated ventilation (NL)
The so-called rated ventilation means the air supply necessary to comply with hygienic and health standards as well as building protection when the apartment is used normally. The rated ventilation level can partially involve the occupant actively in the ventilation concept, for example, with their manual window ventilation.