Phew, regarding the living area. It is already clear that both systems are undersized. I would not go below 350, rather up to 400 (regardless of the manufacturer).
Thanks for the reply! Unfortunately, this does not correspond with my research. The applicable guideline is DIN 1946-6. This defines various room airflows, whereby the controlled residential ventilation must achieve the nominal ventilation.
Moisture protection = fWS * (-0.001 * Ane² + 1.15 * Ane + 20)
Nominal ventilation = -0.001 * Ane² + 1.15 * Ane + 20
Reduced ventilation = 0.7 * (-0.001 * Ane² + 1.15 * Ane + 20)
Intensive ventilation = 1.15 * (-0.001 * Ane² + 1.15 * Ane + 20)
where Ane = area of the usage unit
and fWS = factor to consider thermal insulation (0.3 for new/renovated buildings, 0.4 for all others)
This would result for our house (rounded up) in:
Moisture protection = 0.3 * (-0.001 * 183² + 1.15 * 183 + 20) = 60 cbm / h
Nominal ventilation = -0.001 * 183² + 1.15 * 183 + 20 = 197 cbm / h
Reduced ventilation = 0.7 * (-0.001 * 183² + 1.15 * 183 + 20) = 138 cbm / h
Intensive ventilation = 1.15 * (-0.001 * 183² + 1.15 * 183 + 20) = 227 cbm / h
The Helios can do 315 cbm per hour, the Hoval 300 cbm. Both should therefore be sufficiently sized according to the DIN specification.
We will address the issue again with the heating engineer – he must have had a reason for it, or his offer is based on similar calculations as shown above.