EdelStoff
2021-12-08 21:26:52
- #1
I am grateful for any help.
Exactly, three additional 2 sqm wall heating elements have been installed. They have a flow rate of 1 l/min. I changed the spacing to 10 cm. I just checked the design. The underfloor heating in the bathroom is 110 meters; unfortunately, I don’t have the length for the wall heating elements. I read the flow rate on the heating circuit distributor. The bathroom is adjacent to the HWS, which currently has 22 degrees; no other room, so only exterior walls.
It looks roughly like this, only the pipes for the wall heating are thinner and have an extra circuit:

Exactly, three additional 2 sqm wall heating elements have been installed. They have a flow rate of 1 l/min. I changed the spacing to 10 cm. I just checked the design. The underfloor heating in the bathroom is 110 meters; unfortunately, I don’t have the length for the wall heating elements. I read the flow rate on the heating circuit distributor. The bathroom is adjacent to the HWS, which currently has 22 degrees; no other room, so only exterior walls.
It looks roughly like this, only the pipes for the wall heating are thinner and have an extra circuit: