Now I have to turn to you again because my heating engineer still recommends the ALM 4-12 for me, with a heating load of 5.05 kW (without hot water). Furthermore, he writes that a value of 7 kW is assumed for hot water production. I cannot reconcile this value at all with the common recommendations of 0.25 kW per person per day. Perhaps he means a total demand of 7 kW for heating and hot water combined, but even then I wouldn’t choose the 4-12 variant, right?
For illustration, I have plotted the heating demand (5 kW heating + 1.25 kW hot water) into the performance curves of the iPump ALM 2-8 and 4-12. You can actually see quite clearly that the 4-12 will be constantly cycling at temperatures above -5 degrees because the minimum power is 4 kW. Even the 2-8 variant does not run really efficiently at temperatures above 5 degrees, or do I have a mistake in my thinking? In any case, the bivalence point is outside the corridor recommended by iDM from -3 to -10 degrees in both cases.
It would be great if you could let me know whether I have made a mistake somewhere :)