Might not help you, but yesterday I accidentally came across heating providers online and was surprised that, for example, Vailliant Arotherm plus VWL75 is listed as relatively cheap and available from stock / directly available. What speaks against it?
 

Alessandro

2022-12-08 08:38:50
  • #2
With 11kW you can almost heat a new building with 10 residential units. So it is much too large for your calculation! Did the HB really order that or is he telling you what would be deliverable?
 

Pacmansh

2022-12-08 09:10:34
  • #3
Do you know exactly who ordered it? For us, it was such that a planning office (complete idiots) made the heating design and told the plumber which heat pump to order. At that time, he only had the information about what to order. After he built the heating system and did not follow any (bad) specifications from the planners, I would suspect that he would not have ordered such a wrongly sized heat pump if he had known. If your situation is similar, then I would try to contact the plumber and look for a solution with him. Of course, I don’t know if you can get in touch with him.
 

wp.seeker

2022-12-08 10:44:44
  • #4


nothing speaks against it, all options are being considered.
With Vaillant I still don’t quite get the type designations. How many kW does it have?



If it wasn’t so sad. But exactly that was ordered.



The heat load calculation comes from a TGA office – the heat load calculation is certainly correct, but how he then arrives at 11kW via the Daikin "heating solution navigator" is unclear to us.
The site manager is asking. I wonder if she couldn’t come to the conclusion herself that 11kW is implausible?
The plumber just ordered blindly.
A complete chain of idiots.

We’re building with BT/GC (fluid transitions, depending on what is more advantageous for the company).
So far the company has remained very tight-lipped regarding the heat pump, removing trades, etc. Now they are more open in light of the situation. And then we got the heat load calculation in hand, now all the nonsense comes to light. And of course, everything way too late.
But we can reach the plumber, maybe we can find a solution with him.
There is also a company that installs self-procured heat pumps.
We are looking at various shops to see what is deliverable.
 

wp.seeker

2022-12-08 10:55:49
  • #5
Here are excerpts from the heat load calculation.
The summary of the heat load calculation.

Then picture 2, the excerpt from the heating navigator by Daikin.
There are completely different numbers again; suddenly an outside temperature of -8.6°C is used.

And picture 3
The "solution": the 11 in the middle stands for 11kW

I don’t understand that.

Wärmepumpe.seeker
at the next karma level


 

Tolentino

2022-12-08 11:49:50
  • #6
The Vaillant 75 delivers 7 (7.5?) kW but can modulate very low. However, with large houses, you have to be careful whether the maximum flow rate is sufficient (it only manages 1270). Delivery times are often inaccurate. My experience from last year. Availability is even worse at the moment....
 

Similar topics
02.04.2020Heating load calculation 10.3 kW, is a 9.5 kW air-to-water heat pump sufficient?29
14.10.2022Air-to-water heat pump sizing in new construction311
08.05.2021New construction - floor heating unevenly hot (Vaillant aurocompact)12
09.11.2021Cost maintenance Vaillant Therm plus VWL 75/6 A Height ok?20
04.03.2022Buy / Sell Heat Pump Privately117
30.11.2022Controlled Residential Ventilation & Heat Pump: Viessmann vs. Vaillant vs. Zehnder?47
11.08.2023Purchase advice, heat pump comparison: Daikin or Vaillant?19
28.05.2024Heat pump for new single-family house efficiency house 5512
11.09.2024Which heat pump is needed for an old building?11

Oben