Dipol
2019-07-17 23:10:07
- #1
That was probably asking too much after all, and in case it has not yet been concreted, I will quickly provide standard jargon (quote ) or gibberish (quote ):Whether the installation of the strip steel including the connection tab is standard-compliant or not, I leave it to to explain what was done incorrectly.
- [*] Round or strip steel for foundation earth electrodes is to be installed as a closed ring in the area of the outer walls and not diagonally through the reinforcement. [*] Round or strip steel for functional equipotential bonding conductors in non-earth-contacting floor slabs is to be installed similarly along the outer walls. [*] According to DIN 18014, round/strip steel must be screwed to the reinforcement every 2 m; according to the lightning protection standard series not responsible here, this would only be required every 5 m, but this is also not observed in the photos. [*] In new buildings, hot-dip galvanized connection tabs on foundation earth electrodes are expressly prohibited according to 6.3 Materials for connection components; the lightning protection standards have always required at least insulation at the outlet for hot-dip galvanized strip steel as corrosion protection. In my role as site manager, I would have accepted a round conductor made of steel/galvanized steel in a plastic sheath. [*] According to DIN 18014, measurement documentation is required both for the frost skirt and the floor slab. [*] The standard compliance of the frost skirt cannot be assessed due to lack of pictures; no connections to the reinforcement of the floor slab were visible. [*] Whether at least the floor slab is in earth contact and a ring earth electrode is not required cannot be derived from the pictures.