Controlled residential ventilation supply air in the living area near the sofa

  • Erstellt am 2021-05-29 14:19:23

netuser

2021-05-31 12:50:42
  • #1
Personally, I would prefer to place the supply air in the "left corner," but I assume that with a good=correct design of the system, no draft should be noticeable. At least not in the currently shown position. It was once stated to me that with a well-designed system, no draft is felt!
 

Schimi1791

2021-05-31 13:16:31
  • #2
Reproduction? ...... ...... ...... ......
 

Strahleman

2021-05-31 15:01:28
  • #3
Why only one supply air valve in the large room? Wouldn't two valves in the southern corners be better?
 

guckuck2

2021-05-31 15:40:45
  • #4
Certainly a justified question. With 43 sqm - 2.5m ceiling height, this results in a room volume of about 107.5 cbm. With an air exchange rate of 0.3-0.4/h, the supply air would have to deliver 32.25 - 43 cbm/h. This is usually not achievable with one pipe, so it must be connected twice. The risk of flow noise and drafts thereby increases.

The positioning is also not so perfect to ventilate the room. I would also move the exhaust air from the stove (this is not a second range hood :)).

Maybe better to have a supply air on the left in the corner and one on the right in the other corner of the room. Connect the exhaust air twice and regulate it to 3/4, the remaining airflow goes through the hallway to the upper floor.

Edit: Is the plan complete or is there a missing building part from the ground floor?
 

kasse-tk

2021-05-31 19:54:20
  • #5
No, the plan was not complete, a small office, pantry, and guest toilet were still missing, attached now is the entire ground floor. Yes, the supply air in the living area is supposed to be supplied via two pipes. I don’t remember how it was with the exhaust air in the kitchen. I have marked the idea with the supply air in the corners, did I understand it correctly? And exhaust air kitchen further away from the stove? That actually makes sense, because if the stove sucks downwards and the controlled residential ventilation sucks upwards... that really strains the cook (or rather the cook) :)
 

guckuck2

2021-05-31 20:42:21
  • #6
Fine positioning please coordinate with lamp outlets and smoke detectors, possibly presence detectors. And coordinate with access points. So that nothing collides and nothing hangs all over the ceiling in a mess.
 

Similar topics
06.12.2009Closed or open kitchen?11
22.06.2015Exhaust air / supply air for kitchen hood10
29.04.2016Floor plan single-family house - kitchen problem20
03.10.2016Exhaust air and supply air one above the other?22
27.01.2017Exhaust air vs. recirculated air in a controlled residential ventilation system32
13.02.2017Number of supply and exhaust airflows in residential ventilation11
20.10.2015IKEA Metod Kitchen - Ideas / Suggestions for Planning?29
20.03.2016Start of planning new kitchen22
05.05.2016Is it possible to install Ikea Metod and oven at a height of 50 cm?13
07.06.2016Kitchen Planning: U-Shaped Kitchen and Drawers Collide20
20.04.2017Controlled residential ventilation: place supply air in bedrooms in the wall.23
05.05.2017Central Controlled Residential Ventilation: Supply and Exhaust Air, Door Bottom Gap30
24.12.2017Kitchen: closed or open? What room layout?86
09.01.2018Exhaust air in the bedroom - supply air in the storage room24
17.02.2020Open kitchen: exhaust or recirculation in controlled residential ventilation & KfW5540
15.10.2020Controlled residential ventilation: positioning of supply and exhaust air in my designs44
23.06.2021Controlled residential ventilation - Planning the positions for supply air / exhaust air60
10.11.2021Open kitchen: regret or the ultimate experience?104
19.11.2021Extractor hood: recirculation or exhaust air for KFW55?27
22.11.2021Kitchen consultation: which brand for kitchen and appliances56

Oben