Certainly a justified question. With 43 sqm - 2.5m ceiling height, this results in a room volume of about 107.5 cbm. With an air exchange rate of 0.3-0.4/h, the supply air would have to deliver 32.25 - 43 cbm/h. This is usually not achievable with one pipe, so it must be connected twice. The risk of flow noise and drafts thereby increases.
The positioning is also not so perfect to ventilate the room. I would also move the exhaust air from the stove (this is not a second range hood :)).
Maybe better to have a supply air on the left in the corner and one on the right in the other corner of the room. Connect the exhaust air twice and regulate it to 3/4, the remaining airflow goes through the hallway to the upper floor.
Edit: Is the plan complete or is there a missing building part from the ground floor?