Yes, bad luck is an option.
I understand that a device with a lifespan of 25-30 years can also last only 15-20 years or sometimes even 35-40 years.
But only 6.5 years is really very little and very annoying.
The geothermal heat pump display shows:
Hours: 19672
Starts: 57579
Starts/hour: 35.596
The suspicion of oversizing comes from the specialist company. Let's see how it continues.
I don't want to offend you now, because you have been punished enough with the procurement of the new compressor anyway and I wouldn't wish that on anyone. But your heating system is not maintenance-free and you as the homeowner were not given the operating instructions for no reason.
Who has maintained the heating system? Was it done regularly?
As soon as I saw after the first year that the heat pump starts as shown in the screenshot, the heating technician was at my place the next day. There were just under 9.5k starts on the meter (or one start every 12 minutes). Now, 3 years later, it’s a total of 11.5k starts.
You see, this is not unusual and happens more often, especially when something is defective (RT sensor defective, expansion tank defective, underfloor heating circuits not filled, etc.)