Compressor broken after 6 years (Ecoforest ground heat pump / well construction Heth)

  • Erstellt am 2023-03-24 09:38:55

jx7

2023-03-24 12:25:35
  • #1
Yes, that’s exactly how I would interpret the numbers too and I am just as puzzled.
 

Zaba123

2023-03-24 12:36:11
  • #2

I don't want to offend you now, because you have been punished enough with the procurement of the new compressor anyway and I wouldn't wish that on anyone. But your heating system is not maintenance-free and you as the homeowner were not given the operating instructions for no reason.

Who has maintained the heating system? Was it done regularly?

As soon as I saw after the first year that the heat pump starts as shown in the screenshot, the heating technician was at my place the next day. There were just under 9.5k starts on the meter (or one start every 12 minutes). Now, 3 years later, it’s a total of 11.5k starts.

You see, this is not unusual and happens more often, especially when something is defective (RT sensor defective, expansion tank defective, underfloor heating circuits not filled, etc.)

[ATTACH alt="45D4D8D5-C1AE-4D05-9113-04BB194599FA.jpeg"]79143[/ATTACH]
 

KarstenausNRW

2023-03-24 13:18:06
  • #3
First of all, I also think that the heat pump is too large, even if it can modulate down to 3kW. But when I read that you have 3 times as many starts as operating hours, the heating system is really running badly. Sorry. I would rather expect the ratio to be reversed – at least 2-3 times as many operating hours as starts. If the numbers are correct, the compressor has made as many starts in 6.5 years as a well-running heat pump would in 60-100 years. So the compressor has really held up well (but you probably don't want to hear that). Did no one instruct you on the heating system or set it up correctly? What happened during maintenance, did the installer notice nothing – or did you not perform any maintenance, which I would understand since hardly anyone does.
 

jx7

2023-03-24 13:34:54
  • #4
The heating system was of course set up and we were instructed.

There was maintenance carried out by the installing company, which was included.

The offered maintenance contract was so expensive that we did not sign it, especially since the heating system was offered to us as maintenance-free like a refrigerator before the house was built.
 

SoL

2023-03-24 15:29:12
  • #5

Well, you’re wiser afterwards...
 

jx7

2023-03-24 15:37:48
  • #6
The compressor is not broken now because we didn’t maintain it, but probably because it was incorrectly sized and configured.
 

Similar topics
20.10.2016Water-bearing fireplace stove floor heating, heat pump, photovoltaic, new construction?28
26.08.2015Cost Breakdown Heat Pump - Heat Pump with Ground Collectors23
19.05.2021Experiences with brine heat pump491
08.06.2017Photovoltaic system, how to use experiences like heat pumps?64
23.10.2016No heating is approved?!15
03.01.2017Preparation for photovoltaic or solar thermal with air-water heat pump18
14.09.2018Heating (Heat Pump) Incorrect, heat output too high?14
25.03.2019Electricity consumption air-to-water heat pump20
22.11.2019Heating offer comparison - Please share your experiences49
08.10.2019New heating system with hot water preparation?!20
05.11.2019Which heat pump to use in monolithic construction?33
11.12.2019Gas heating or heat pump air (Mitsubishi?) or groundwater16
02.03.2020Incorrect heating installed — problem and consequences?25
11.06.2021How much does a good new heat pump cost? Looking for experiences!58
24.08.2021Cooling with heat pump via underfloor heating?117
01.06.2021Local heat or air-water heat pump?11
14.06.2021Separate meter and electricity tariff for air-to-water heat pump sensible?103
07.06.2021Installation of heat pump/heating - before or after screed16
05.07.2022Renew old heating with heat pump or gas boiler and domestic hot water heat pump58
07.10.2023How to plan heating with a heat pump in new construction?14

Oben