The CoP value or the annual performance factor are of course completely irrelevant to the question of whether this heat pump is properly/well sized. Nevertheless, certain values must be achieved (specifically for the location of the planned use) in order to obtain any potential funding.
However, if your heat pump has a nominal output of 8.1 kW at 7 degrees outside temperature and 35 degrees flow temperature, then it will presumably be significantly lower at -12 degrees outside temperature. So if the heating load calculation is correct, it could be a close call once it gets really cold or an expensive one if the electric heater runs then.
However, if your heat pump has a nominal output of 8.1 kW at 7 degrees outside temperature and 35 degrees flow temperature, then it will presumably be significantly lower at -12 degrees outside temperature. So if the heating load calculation is correct, it could be a close call once it gets really cold or an expensive one if the electric heater runs then.