Air-water heat pump in KFW55 house / heating load, standards?

  • Erstellt am 2021-05-02 23:33:04

Bookstar

2021-05-03 11:02:36
  • #1
We actually had these temperatures for weeks this winter, but the heat pump was hardly ever above 32 degrees flow temperature. And such winters are extremely rare. Just like this spring, last night it was 0 degrees again and single digits during the day. It’s annoying and burns energy endlessly, climate change!! :D
 

tomtom79

2021-05-03 11:40:52
  • #2
How can you have 550m2 heat transfer but only 700m3 air volume?

I don't understand that or are window areas included?

And better calculate with exact room temperatures.
That means in the bathroom 23-24 degrees
Living room/kitchen 22
Children's room/bedroom 20
Office 22

Better higher temperatures than a heat pump that has to deliver more.

If it must be a heat pump, tell the heating engineer to keep a maximum 7cm pipe spacing for the underfloor heating in the bathroom and maximum 10cm in the other rooms.
No additional heating in the bathroom.

And supply temperature not above 30 degrees

But others have already written that.
 

Similar topics
28.08.2013New single-family house, gas or heat pump, target KfW5529
12.09.2014Domestic Hot Water Heating vs Efficiency of Air-to-Water Heat Pump11
19.09.2023Cooling via underfloor heating with brine heat pump45
19.05.2021Experiences with brine heat pump491
14.10.2017Heat pump flow temperature experiences?13
30.12.2017Heating system new construction (heat pump + stove + solar)35
15.01.2018Is nighttime lowering of the heat pump sensible?13
17.04.2018Heat pump domestic water storage tank - What size is recommended?12
22.11.2019Feedback on heat pump / offer requested!46
12.01.2021Underfloor heating air-water heat pump. House too warm when the sun shines690
20.12.2019Difference in purchase cost between gas pump or heat pump74
27.01.2020Properly setting the air-to-water heat pump with underfloor heating54
07.01.2020Is there still a need for a solar system at all with air-water heat pumps and photovoltaics?24
02.04.2020Heating load calculation 10.3 kW, is a 9.5 kW air-to-water heat pump sufficient?29
19.03.2021Combine air-water heat pump with water-carrying wood stove57
14.10.2022Air-to-water heat pump sizing in new construction311
04.01.2022Air-water heat pump current consumption and data1439
02.01.2022Hydraulic balancing air-water heat pump + efficiency circulation pump109
18.09.2023Optimization of heat pump LWD 70A with photovoltaics16
11.11.2023Heat pump in the transition period34

Oben