The actuators are missing here. Or the heating installer is knowledgeable and only performed the thermal balancing via the valves.
I wouldn’t use any if the upper floor is now to be heated permanently, but instead set them manually. Of course, this only works if the heating curve fits; otherwise, you have to lower that as well until it fits.
The blue caps are actually "construction caps" or manual controls. The further you turn them in, the less flow there is. Fully up or "off" means fully open.
I would first open them all and then see how everything behaves. Especially whether enough reaches all heating circuits on the ground floor and if there is enough flow everywhere. If anything doesn’t fit: turn down where there is too much and wait another day, etc.
If necessary, do the same for the heating circuit distributor on the ground floor if the valves there are throttled too much.