KlaRa
2016-08-16 18:06:04
- #1
Hello Matthias. The edge chamfers, which ultimately led to a flank tear of the elastic sealant between the baseboard tiles and the tile surfaces, are due to overnight drying of the screed and its associated re-curling towards the insulation layers. You only mentioned in your post that the tiles were hollow. However, with large tile formats, as I can see from the photos, at least when the tiles are laid using the thin-bed method, there cannot be a 100 percent support and thus not a 100 percent backside wetting of the tiles. This would only be possible when laying with the medium-bed method due to the greater adjustment possibilities. This is simply because the tolerance-compliant unevennesses of the substrate argue against it with the larger formats. So if the large-format tiles are only partially (35 % to 40%) hollow, that alone would not be a reason for concern. However, it could become problematic if the tiler did not perform a residual moisture measurement on the screed before carrying out their work. But I do not want to open another issue at this point! It should therefore be noted that the flank tears of the elastic sealant under the baseboard tiles are not a cause for concern and occur in many other new buildings. That is why such joints are also referred to as so-called maintenance joints, the ongoing inspection and, if necessary, renewal of which are the responsibility of the builder or the user of the property.