I have looked at the drawing(s) several times.
The way " " evaluated it is how I see it as well. Why?
Above the 25cm thick reinforced concrete ceiling, the continuous insulation and load distribution layer with 3.15m - 2.85m = 30cm was taken into account.
If we turn to the interior area, a 25mm (2.5cm) impact sound insulation will be sufficient due to own use, plus 4.5cm screed = 7cm freely available build-up in the interior area. Here, 2cm lightweight leveling screed, PE cover foil + 5cm cement screed would be conceivable.
Now to the exterior area:
We also have 30cm build-up height here, as I see it.
In addition to a sealing layer (approx. 3-5mm), we need 10cm thermal insulation and still have about 20cm for the top layer with leveling.
If we take a 4cm thick concrete stone in a gravel bed, about 16cm remain of the 20cm for a cover (on the insulation layer) and the gravel bed.
That’s always enough!
Therefore, I also do not understand why a large area should be filled multiple times with screed, a completely nonsensical and impractical approach from my point of view, which also touches on static aspects.
Am I maybe seeing this wrong?
--------------------------------
Regards: KlaRa