Oetzberger
2021-10-02 16:46:59
- #1
I looked at the brochure; the 15 and 20 models seem essentially identical, both have a minimum output of 4.5 kW. The 15 will be more than enough, but the 20 is technically just as suitable. I think, for psychologically irrational reasons, I would simply take the 20 at a slightly higher price and be done with it, but it’s rather a meaningless oversizing. The 25, on the other hand, has far too much minimum output and would be a big mistake.
P. S.: Probably the 10 would also be sufficient in practice and even fit better, but first, the heating installer wouldn’t agree to that, and second, there’s no need to overdo it. A well-balanced underfloor heating and then the 15/20 fit perfectly.
P. S.: Probably the 10 would also be sufficient in practice and even fit better, but first, the heating installer wouldn’t agree to that, and second, there’s no need to overdo it. A well-balanced underfloor heating and then the 15/20 fit perfectly.