That is in the counteroffer. But as a dummy, I can't interpret it.
Not 60,000 kWh, but 6,000 liters of oil consumption.
Because with the heat pump the supply temperature is only 45 to 50 degrees, and with oil I sometimes had almost 60 degrees.
The picture shows that below -7°C the heating rod has to provide additional heating. In your area, the NAT is probably around -13°C, so quite a bit still goes out with a COP of 1.0, which is pretty inefficient.
1 liter of oil has about 10 kWh of heating power, if the burner wouldn’t blow anything out the chimney.
The logic of radiators plus air conditioning is a bit weak: if the outdoor unit delivers a maximum of 15 kW, the air circulators won’t bring more power into the rooms either. The delivered power must somehow be shared between the radiators and the air conditioning units. So even less remains for the radiators than if they were alone. It would be different if you complemented a heat pump with a separate air conditioning system: then you have two independent heat generators.
You also don’t necessarily have to replace all the radiators. Search for the tool Heizreprot. For little money you get a qualified statement about which radiator needs which supply temperature to keep the room warm. Then you replace the worst radiators and maybe move some from one room to another.
Measuring rooms and radiators is no rocket science, and the different radiator types are also relatively easy to distinguish.