First of all, thank you to everyone.
meaningful pictures of the RC gravel (close-up, overall, high resolution)
Photo is attached
The soil surveyor was here today and said that our installed RC gravel has a very high sand content. He suspects it's too high. He took a bucket full with him and is analyzing it. Feedback is still pending.
The specifications for 40cm RC gravel, installed and compacted in two layers, come from the soil surveyor.
Does the vibrating plate "float" while compacting on the ground?
I don’t quite understand what you mean by that?!
The question is what was required, 80 MN/m² is common for a single-family house.
Yes, the 80 MN/m² is required, as well as the value of <2.5 EV2/EV1.
But unfortunately, it is about the warranty in case of occurring damage... whatever causes it.
Yes, understandably, the shell builder will not start for warranty reasons as long as the values are not met by the contractor.
So, what could the problem be...
Wrong grain size distribution (values are good, compaction is not).
Grain size distribution 0-32mm, as already mentioned above with too high sand content?
wrong equipment, wrong operation, too little water, too much water)
The vibrating plate is a Wacker DPU weighing about 550kg. The civil engineer thinks that is completely sufficient.
This week they even went over it again with a 1.2-ton roller as a precaution. Without success...
What is too little or too much water? Both layers were watered and compacted. Possibly with too little water. Unfortunately, it has not rained at all in the last two weeks, and hardly before that either.
I would call the soil surveyor and ask for his opinion. He recommended the setup and knows the subsoil.
Yes, his response is still pending.