Yes, Lex is right - using our bathroom on the ground floor as an example:
Heat loss at -12° C [W]: 140
Design temperature [°C]: 24
Heatable area [m²]: 3.7
Theoretically required W/m²: 37.84
Laying distance at 30°/26° [cm]: 5 cm -> results in 13 W/m² (no more possible)
Notes: Heatable area -> 4.7 m² minus shower
One should consider that 30/26 is extremely low for the calculation and -12° only occurs every 10 years. Furthermore, the 13 W assumes that there is a carpet on top and the air cannot circulate freely.
The area simply is not sufficient here - even with a 5 cm laying distance.