KingJulien

2024-01-18 08:43:01
  • #1
We also had the whistling HKV, as handed over by the GU. This comes from heavily throttled circuits. Here you have high flow velocities, which then cause the whistling.

So turn everything fully open (at the sight glasses AND under the ERR caps), close any existing bypass valve, always keep all ERR fully open or remove them immediately.

Then perform the balancing. It reads more complicated than it is.
 

jens.knoedel

2024-01-18 09:03:32
  • #2

In new buildings, always heat all rooms evenly.

P.S. It is a misconception that you only heat 80 sqm. By heating with 80 sqm of heating surface, you are actually heating the entire house. It's like a refrigerator—you can't say that you don't cool the middle shelf.
And with that, you have messed up the heating settings = the problem you described.
 

NewHouseAppear

2024-01-18 09:17:10
  • #3


One question regarding this: we also have a heat pump + underfloor heating in a new building with a basement, where there is a relatively large living area that can also be heated, while the rest of the basement cannot.
As you suggest, we have all heating circuits fully turned up and regulate via slope and heating curve directly at the heat pump. The temperature in the house is fine as well. But I wonder whether it still makes sense to heat the large basement room (where we basically do not stay) or if we can confidently turn it down without encountering the problem you described.
Are there any universally valid answers on this?
 

jens.knoedel

2024-01-18 09:34:12
  • #4
Actually not. There are many points of relevance: basement completely insulated (I assume)? Insulation under the underfloor heating on the ground floor (which/how much)? Connection from basement to ground floor? etc. But you only have one room. Just try what happens if you turn the room off completely. It may be that you then have to adjust slightly overall.
 

Eldirwars

2024-01-18 09:44:52
  • #5


Why do you have to compensate for the other rooms? The hydraulic balancing was done, the flow rate was adjusted again by the heating engineer yesterday. If I also leave the thermostat at 15 degrees in unused rooms, then the room does not heat either, right?
Many others I talk to tell me that you don't hear anything from the manifold at all. The noise is also better in the morning or at night. In the evening it is always strongest, which surprises me a lot.
 

Eldirwars

2024-01-18 09:51:28
  • #6


Am I supposed to open each valve to full flow and let every room be flushed with the full amount? Doesn’t that also increase consumption? I have to google what the ERR caps are and possibly adjust them, also the bypass valve.
It’s just that whenever I stand in front of the box and open different valves, it always gets louder depending on how much I open. Opening all completely would mean extremely loud.
 

Similar topics
20.10.2015Underfloor heating on the ground floor and upper floor, radiators in the basement?15
25.11.2015Offer air-water heat pump including underfloor heating, ok?19
17.02.2016KFW 55 in semi-heated basement - cold basement31
15.04.2016Is the cost of underfloor heating completely exaggerated?44
20.06.2016Gas or Air-Water Heat Pump16
09.12.2016Single-family house with basement - optimization suggestions?12
20.12.2019Underfloor heating in the children's room? Some rooms planned without underfloor heating? Air-to-water heat pump removed?48
20.03.2021Basement underfloor heating or low-temperature radiators22
01.06.2021Local heat or air-water heat pump?11
17.07.2021Underfloor heating and air-to-water heat pump in new construction: am I going to have problems?28
08.10.2021Air-water heat pump combined with underfloor heating does not work properly65
10.11.2021Is underfloor heating in the basement useful??60
03.01.2022Geothermal heat pump single-family house 200m² underfloor heating kfw55 - setting/optimization91
12.04.2022From when is a heat pump worthwhile in an old building?13
14.05.2022Old building apartment with gas boiler - underfloor heating now, heat pump later14
16.04.2022Which air-to-water heat pump is suitable for new construction?13
25.05.2022Air-to-water heat pump + underfloor heating + controlled residential ventilation with heat recovery - individually room differently temperature controllable?10
14.01.2023Internal heat pump in the basement not possible due to groundwater?37
02.02.2023Individual room control with air-water heat pump and underfloor heating20
26.06.2023Heat pump, water storage tank, instantaneous water heater, wfK, underfloor heating, heating and cooling12

Oben