Yes, that is precisely one of the problems, normally it goes like this:
- You put 16A circuit breakers in the distribution board
- Lay 3x1.5 or 5x1.5 cables to all the sockets in the house (no matter how far they are or in which medium the cable runs)
- It is measured and everything seems ok
But when a bunch of devices are later connected to the mentioned line, the user has a problem... but he doesn't know about it because he always relies on the 3600 watts...
Without considering losses etc., 1.5mm² and 16A is the limit at 18m... and that is reached faster than you think, especially if the distribution board is in the basement.
That’s why it’s better to have a few more sockets + circuits, then there is still room for expansion...