Central controlled residential ventilation with heat recovery: Are rooms individually controllable?

  • Erstellt am 2015-04-23 11:59:13

nordanney

2015-04-23 20:52:43
  • #1
Isn't it normal that in summer the air is not further heated, but there is "only" ventilation?
 

Sebastian79

2015-04-23 20:53:58
  • #2
Yes and no, it should be normal, but there are still some systems that don't have a bypass... we have one in the rental place :/
 

nathi

2015-04-23 20:55:18
  • #3


The heat pump of course does not run then, but ideally you also avoid heat recovery.
 

LuciferSam

2015-04-24 07:56:49
  • #4
First of all, thank you very much for your feedback!

Ideally 18°C, which of course is not achievable in summer. As cool as possible. But in summer I want to cool the whole house at night anyway, so the problem lies rather in winter. Of course, heat is also transferred through briefly open doors, walls, etc., but I don't want to worsen the problem by active compensating ventilation.

Hmm, I can't find any real definition of a constant volume flow controller anywhere. If it does what the name says, then it's rather the opposite of what I want. The volume flow should adjust dynamically and not be kept constant.

Ah ok. Thanks for the tip, I will look into that.

In general, you are right - a huge effort is made to achieve a state that is quite similar to a conventional house without central controlled residential ventilation. I will continue to think about it...
 

Mycraft

2015-04-24 10:17:45
  • #5
So I can tell you from my experience... what you are planning is relatively pointless... air is a poor medium and with a [Kontrollierte-Wohnraumlüftung] neither acceptable cooling nor heating results can be achieved without additional cooling or heating...

That is why you won’t find anything on the topic, because it simply doesn’t make sense...

And as Lex already wrote, the bypass is only of little help...

A [Kontrollierte-Wohnraumlüftung] is neither an air conditioning system nor a heater... it only provides fresh air and the temperature differences at the valve are negligible when the underfloor heating is running and the sun shines into the room during the day...
 

LuciferSam

2015-04-27 07:23:23
  • #6


I have tried to roughly estimate this.

Assumptions:

    [*]In a room at T1=18°C, air at temperature T2=21.5°C is blown in (while air at temperature T1 escapes through slots in the door).

    [*]Two people are sleeping in the room; a recommended airflow is about I = 50 m³/h = 50/3600 m³/s.

    [*]The density of air is rho = 1.293 kg/m³.

    [*]The specific heat capacity of air (at constant pressure) is cp = 1005 J/(kg K).

    [*]The heat power brought into the room through air exchange is A = cp * I * rho * (T2-T1) = 63 J/s = 63 W. (Compare the first formula in the Wikipedia article on specific heat and note that 1 joule = 1 watt-second.) (This, of course, only applies as long as the room temperature is 18°C. The power is proportional to the difference T2-T1 and thus decreases as the room warms up.)

I estimate the heat output of a sleeping adult at about 40W to 80W (ask Google), so quite comparable to the heat output of the ventilation.

The ventilation system is therefore a poor heater if you compare it to a radiator. But it is a good power output compared to a human and thus quite relevant!
 

Similar topics
27.02.2013Controlled residential ventilation or regulated air - experiences?14
30.04.2015KFW70 with gas-solar heating65
15.12.2015Exhaust hood in controlled residential ventilation: Your experiences?30
09.05.2016Compliance with the 2016 Energy Saving Ordinance with the following heating14
21.01.2016Is the heating oversized?44
25.01.2016Which heating system would you choose for our planned new building?15
29.04.2016Which heating? Please provide recommendations27
09.09.2016Controlled residential ventilation and still open windows at night71
30.12.2016Geothermal heat pump with controlled living space ventilation or without18
04.06.2017Which type of controlled residential ventilation are we?10
27.11.2017Ventilation system with heat recovery, installation location temperature11
06.02.2018Solar for hot water/heating or better photovoltaic for electricity?21
10.02.2018Controlled residential ventilation or photovoltaic system? Seeking decision support, pros and cons18
01.09.2018Offer for heating / sanitary / ventilation - is it realistic?55
04.09.2018Pantry: Is a heating coil sensible in controlled residential ventilation?14
11.10.2018Integrate cooling into controlled residential ventilation or have air conditioning separate?14
01.07.2019Which heating system for the 200 sqm new building?54
17.11.2019Manufacturer heating / controlled indoor ventilation wanted10
05.09.2024Split air conditioning and controlled ventilation with heat recovery44

Oben