According to which standard is your house built? I assume you currently have a cozy 19°C inside the house?
Currently, I have around 20°C, which would be OK except for the bathroom where it can definitely be around 21-22°C.
KFW 55 air-water heat pump with underfloor heating designed for a maximum flow temperature of 30°C at NAT -12°C. Everywhere VA 10 piping is installed for the underfloor heating.
Yes, that won't work. You will have to run a higher flow temperature. Where does that assumption come from?
I’m trying to find my way because it’s not cold enough yet, so I can’t do a proper balancing of the underfloor heating.
If I run the system continuously 24/7, it cycles too much for me.
Currently, I have the heating enabled for 8 hours during the day (because there is also photovoltaic on the roof) and get 3 compressor starts and 7 hours of runtime.
If I run the heating continuously, I have about 15-20 cycles per day.
Heating curve is set to 0.15 with a desired temperature of 22°C.