Joedreck
2017-12-27 07:50:01
- #1
Then I really don't understand it. I also cannot reproduce it in the U value calculator.
The losses in general are of course clear to me. It is also clear to me that with a higher temperature gradient the losses are higher as well.
A floor heating system running 24/7 (as it should be) will have a constant temperature anyway (under the same conditions). The only thing with a thicker screed is the time it takes for the screed to heat up.
And I could not reproduce the then higher surface temperature either.
The setup was from bottom to top
Ground 0 degrees
Concrete 2% 20cm
Bitumen sheet
10cm XPS
Foil
Screed as heating layer
Water temperature 35 degrees 10cm pipe spacing
When I changed the screed from 6cm and 4cm coverage to 60cm and 54cm coverage, nothing changed in the calculator regarding the surface temperature. Why should it, the heating continuously supplies energy and the losses of the component are the same since the other parameters remain the same.
Probably the screed is too good a heat conductor to change anything there.
Admittedly, if instead of screed a 1cm XPS board were placed ON TOP or a 20cm board, it would of course make a very big difference. With screed probably not, or the calculator really cannot represent it.
The losses in general are of course clear to me. It is also clear to me that with a higher temperature gradient the losses are higher as well.
A floor heating system running 24/7 (as it should be) will have a constant temperature anyway (under the same conditions). The only thing with a thicker screed is the time it takes for the screed to heat up.
And I could not reproduce the then higher surface temperature either.
The setup was from bottom to top
Ground 0 degrees
Concrete 2% 20cm
Bitumen sheet
10cm XPS
Foil
Screed as heating layer
Water temperature 35 degrees 10cm pipe spacing
When I changed the screed from 6cm and 4cm coverage to 60cm and 54cm coverage, nothing changed in the calculator regarding the surface temperature. Why should it, the heating continuously supplies energy and the losses of the component are the same since the other parameters remain the same.
Probably the screed is too good a heat conductor to change anything there.
Admittedly, if instead of screed a 1cm XPS board were placed ON TOP or a 20cm board, it would of course make a very big difference. With screed probably not, or the calculator really cannot represent it.