Sparfuchs77
2020-12-08 13:12:36
- #1
The house is located in the Westerwald, where it used to get colder in winter (-12°C to -15°C). The calculated heating load for 100m2 of living space is just under 3.5 kW.
For comparison, since I would like to address more of your statements:
- We built according to the Energy Saving Ordinance and, according to the design, have just under 6 kW heating load for 170 sqm. Underfloor heating with gas boiler. Planned was 24cm KS + 16cm ETICS 0035. We installed 0032 ETICS.
Forget about having 24°C in the bathroom and only 18°C in the bedroom right next to the bathroom—you will achieve a maximum of 2°C temperature difference between individual rooms if at all.
Is that because of the heat pump? We have the heating in the bedroom set to 3, which results in 18 degrees, and the adjacent children's room has 22 degrees during the day and 19 at night.
Underfloor heating should be designed at max. 30°C flow temperature based on the NAT... and not 35°C
NAT = standard outside temperature? For us, that is -13 degrees. Do I understand correctly that when it is -13 degrees outside, you have a warm house with a 30-degree flow temperature? (22 in living areas and 24 in the bathroom?) I already had 37°C on the boiler at -4 degrees.