Underfloor heating distance, missing spot, and bathtub

  • Erstellt am 2019-06-23 14:39:30

M4rvin

2019-06-23 14:39:30
  • #1
Hi,
I wasn’t exactly sure in which subforum to write...

Our site manager asked me whether we want to place the bathtub on the screed or on the concrete. We hadn’t really thought about it so far, but we decided on the concrete floor.
In any case, I was just on site and cut away the styrofoam since the screed work starts on Monday.

I noticed a few things:

1) What is the maximum spacing allowed for the underfloor heating pipes? To me, some distances of 30 cm seem quite large.
2) Is it common to simply leave some spots out? (Like in front of the bathtub, see picture)
3) Where I cut away the styrofoam around the bathtub, there are still some pipes—don’t they cause any issues? And why is such unstable styrofoam placed between the floor and the screed at all?

Thanks in advance
Marvin


 

boxandroof

2019-06-23 15:25:37
  • #2
This should be calculated beforehand based on a room-specific heating load calculation and not estimated. In the bathroom, usually a very close spacing is used, 10cm or less if you plan with a low supply temperature. However, it depends on the conditions, so the statement should be seen only as an example. Especially if you have a heat pump, it is very important to plan the bathroom well; otherwise, you will have to operate the entire system for all rooms with lower efficiency/higher supply temperature just because of the bathroom.
 

M4rvin

2019-06-23 16:16:41
  • #3
Ah ok, thanks! Yes, we have a heat pump. So I assume that everything has been calculated correctly? I just sent another email to the installer, let's see what he says.
 

boxandroof

2019-06-23 16:21:40
  • #4
The spacing seems too large to me. Have a room-wise heating load calculation and installation plan handed over to you. The flow temperature should be planned at a maximum of 30 degrees.

It will get warm enough, but the annual performance factor/electricity consumption suffers if a room is significantly undersized. Usually, it is the bathroom because there is little space available there anyway due to the tub/shower.

In the 15m2 bathroom, we have two 80m circuits with 7.5cm spacing. A circuit should not be longer than 100m in case you have any changes.
 

M4rvin

2019-06-23 16:26:24
  • #5
All right, I’ll follow up on that! I’ve just quickly uploaded a video, but now I’m not sure if I’m allowed to post it... If not, I’ll remove it again.

[MEDIA=YouTube]XpfchMEQim4[/MEDIA]
 

Bookstar

2019-06-23 17:24:02
  • #6
Overall, it is laid very neatly. The door transitions are also protected, and it was laid into the door recesses as well.

Not so nice, however, is that some spots, especially corners, were left out. But that is forgivable.

The gaps also look OK. Less than 10cm doesn't make sense, I would recommend 15cm for the bathroom and 20cm for the rest.

So I would say you can be satisfied with the installation.
 

Similar topics
09.06.2015Gas, heat pump, and solar for a single-family house?36
04.09.2015What height bathtub?17
24.06.2016Which storage should be used with an air-to-water heat pump?16
24.06.2016Question about heat demand determination and flow temperature11
05.01.2017Bathtub in front of the window - parapet height?14
05.04.2017Super disaster - water pipe burst, screed damp31
17.04.2018Heat pump domestic water storage tank - What size is recommended?12
08.03.2018Is heating load calculation with desired temperatures necessary?14
23.01.2020Towel radiator for air-water heat pump22
02.04.2020Heating load calculation 10.3 kW, is a 9.5 kW air-to-water heat pump sufficient?29
05.06.2020Heating load calculation or room heating load26
14.10.2022Air-to-water heat pump sizing in new construction311
07.06.2021Installation of heat pump/heating - before or after screed16
08.10.2021Air-water heat pump combined with underfloor heating does not work properly65
21.06.2022Renovation of heating system for existing property - condensing boiler/air-water heat pump/DHW heat pump25
23.09.2022Sanitary shell inspection: What should we pay attention to?46
17.10.2022Heating screed with device vs. with heat pump: costs?19
25.11.2022Mill underfloor heating or apply new screed?17
16.03.2023Lowering the supply temperature in underfloor heating more complex than expected?70
24.11.2023Heat pump: buffer tank, capacity and modulation46

Oben