Dipol
2019-10-13 15:44:16
- #1
Finished so far.
Just connect the 16 mm² cable from the equipotential bonding at the distribution block and continue it up to the antenna mast.
Not 16 mm diameter but 16 mm² cross-section.
Grounding conductor made of 16 mm² Cu in solid as well as heavy, difficult to fix multi-strand design must be connected to the antenna support with Class H connectors certified for 100 kA for the wire type used, such as
[*]Band clamp DEHN 540 103, OEM also KATHREIN ZEU 168
[*]Band clamp PRÖPSTER 111 393
and must not be cut through a PAS, of which according to the test report available to me ONLY the outer clamps for band and round steel Class N = 50 kA are certified and the middle clamps for 16 mm² Cu are not tested at all. This PAS would weaken the lightning current carrying capacity and is not needed for the equipotential bonding of the earth block, earth angle, and EXR housing on the grounded antenna support, so better remove it.
Also, at the grounding conductor’s termination point, an HES for lightning protection equipotential bonding with tension clamps and connection to a standard-compliant earth electrode is required if it is not to become one of the unfortunately common cosmetic groundings with questionable lightning current carrying capacity.
If your fingers, maltreated by technically outdated F screw connectors, still allow it, the LNB cables should be laid as a loop, because otherwise, they are hardly removable. For the next antenna installation, use finger-friendly connectors according to the state of the art or at least a screwing aid.