Potential equalization for satellite must be laid separately

  • Erstellt am 2017-10-03 01:16:07

winnetou78

2017-10-10 17:11:41
  • #1


What do you say about that? Thanks for your help,
 

Dipol

2017-10-10 17:58:03
  • #2
No one points out more often than I do that, according to NAV § 13, installations of grounding and equipotential bonding are reserved for licensed electrical specialists.

Given the fact that only a few antennas installed by licensed electrical specialists are even 100% standards-compliant, this also takes some overcoming. Yes, that would be a standards-compliant GROUNDING, provided, exceptionally, that the connections on the roof rafter bracket and the grounding system are certified to withstand 100 kA lightning current. 16 mm² copper wire can withstand monster lightning strikes of 200 kA, subject to clamps designed for that purpose.

Actually, you do not do that yourself, because you are not a licensed electrical specialist, see above.

    [*]Grounding conductors must be clamped to masts or the vertical pipe of roof rafter brackets using lightning-current-resistant class H certified grounding clamps. So far, there is no roof rafter bracket with a certified clamp for grounding conductors.
    [*]If the grounding conductor is connected to a main earthing terminal (HES), it must be one designed for lightning equipotential bonding and not, as is often the case, Elis’s favorite busbar for power equipotential bonding according to VDE 0100 standard series.
    [*]The equipotential bonding of cable shields is connected via grounding block or grounding angle and with 4 mm² copper that is not lightning-current resistant to the grounded point; likewise, housings of mains-powered components, especially multiswitches (even if located in the basement).
    [*]For that, the usual banding grounding clamps with an M6 screw and clamp plate suffice; a properly installed cable lug on an M5 screw also works.
Pictures say more than words. Unfortunately, the system currently shows me that I do not have the rights to upload them.
 

winnetou78

2017-10-10 18:16:24
  • #3
Too bad, thanks anyway.

Ps sometimes it is better if a layman does it after a lot of reading and asking about standards or DIN, than a so-called electrical specialist who does it the way he always has. I asked 2 electricians, both said, put the Sat up and done [emoji45]
 

Dipol

2017-10-10 19:09:47
  • #4
You are not the first layperson who is more knowledgeable about standards regarding grounding and equipotential bonding than some electricians after contacting the forum. If the announced revision of IEC 60728-11 goes through in my favor, it will not change anything for the two standard-free electrical "professionals", because they won't notice the changes.
 

winnetou78

2017-10-10 19:22:14
  • #5
I think so too. But that exists in many areas, I just mention [Sauberkeitsschicht], I have been looking at at least 30 floor slabs for half a year, all had bubble wrap.
 

*Dipol*

2024-04-28 01:37:55
  • #6
Since I happened to come across the old topic by chance, here is a supplementary example image from the currently valid DIN EN IEC 60728-11 (VDE 0855-1):2023-10:



Grounding conductors made of 16 mm² Cu, 25 mm² aluminum, or 50 mm² steel per se also withstand rare lightning strikes exceeding 200 kA. However, every chain is only as strong as its weakest link, which is why antenna grounding can only fulfill their intended lightning protection function if the connectors for the respective grounding conductors used are also certified according to the highest test class H with 100 kA.

The requirement that accessible grounding conductors must be installed in a PVC empty conduit with a wall thickness of 3 mm has been removed.
 

Similar topics
28.02.2013Heat demand calculation according to DIN 1283112
24.03.2014Heating proof: Heat load calculation according to DIN 12831 or DIN 4708?10
10.09.2015DIN 4109 Noise - What is to be considered?13
28.11.2016Is sound insulation according to DIN standard 4109 relevant for building permits?16
02.06.2016Sat multiswitch in the attic or basement?22
09.11.2018Is installation of surge protection according to DIN VDE 0100-443/543 mandatory?15
04.07.2017Lightning protection at the house, but how?12
12.10.2017Installation of satellite dish on the roof61
18.10.2018Construction costs for terraces, etc. in cost estimation according to DIN 2719
26.01.2019Proper grounding in steel fiber concrete and black tank11
17.11.2019Satellite system - buying guide and installation41
14.05.2020Sound insulation VDI Guideline 4100 & DIN 4109 in prefabricated house construction49
24.11.2020Heating load calculation & layout plan DIN: Is a new calculation necessary?41
23.04.2023Is preparing for photovoltaics in new construction sensible?81
27.06.2023Is sound insulation according to DIN 4109-1 sufficient for a mid-terrace house?19
15.12.2022Planning guest WC in new construction - How big should it be? (DIN?)107
27.12.2022Door DIN left or right – are both possible?17
07.11.2024Is window planning mandatory according to DIN 5034-2021-08?13
20.11.2024Is staircase DIN 18065 mandatory or not?82
14.02.2025The planner does not perform any calculations according to DIN 27660

Oben