Ah ok. What is the equipotential bonding? I already live in it and my electrical installation has already been approved, my satellite system was also installed by the electrician. Therefore, everything should be grounded anyway. So what were the steel wires at every corner of the house for? What is the point of them sticking out? What is HAR? I don’t have an external lightning protection system. After reading this, it makes absolutely no sense to ground the gutters.
 

Mycraft

2017-07-02 00:53:21
  • #2
Yes, you understood correctly, without an external system you can leave the gutters as they are.

HAR = house connection room

The flags were at four corners possibly because the executing electrician did not know where the HAR would be located...(pure speculation)

Potential equalization is the technical term for the grounding of the house. However, it is not protection against lightning strikes etc., but necessary according to IEC 60364-4-41:2005 and for Germany DIN VDE 0100-410:2007-06.
 

meister keks

2017-07-02 05:50:37
  • #3
Thank you very much for your information.
 

Kaspatoo

2017-07-02 10:40:03
  • #4
The following was specified by our electrician:
- continuous foundation earth conductor, as well as one running across the slab (so that semicircles are formed from the mentioned ring wezi)
- a flag in the HAR for the internal house grounding
- a flag at each corner of the house to install a possible external lightning conductor (currently not planned, so currently only in preparation)

From other (older) houses, I know (from seeing) that at least two steel bands from the lightning conductor on the roof are connected to such a flag each

Whether a connection to the gutter is sensible or possible, I cannot judge

If the thread starter now has a lightning conductor on the roof, then I think one connection is not enough; if he doesn’t have one, cutting it off is probably irrelevant
 

Dipol

2017-07-03 21:10:34
  • #5
Lightning protection is by definition the sum of all measures, divided into external and internal lightning protection. The equating of lightning protection with a lightning protection system has long been outdated.

The internationally harmonized lightning protection standard series IEC 62305, German classification DIN EN 62305 (VDE 0185-305) and in Austria the - except for the national foreword - identical ÖVE-EN 62305, apply only to buildings with lightning protection systems.

Conventional lightning protection systems must have at least two down conductors; only one would be non-compliant with the standard.

The integration of gutters and the base of downpipes is mandatory in lightning protection systems, but otherwise optional.

Separate ground electrodes totally contradict the basic principle of equipotential bonding and are dangerous and non-compliant with standards. Even under very old ABB regulations, they were only permitted under strict restrictions exclusively for lightning protection systems, but have always been prohibited for antennas.

Equipping rainwater downpipes with their own ground electrodes is less dangerous than pointless.

Agreement, since "external system" means external lightning protection.

Objection!

Since I currently have my "house standard" at hand, I copy the official terms according to IEC from it:
 

Knallkörper

2017-07-04 01:06:42
  • #6


Non-compliant with standards, perhaps. I naturally assume that there is no lightning protection system in the proper sense. Rather not dangerous, or what is the physical explanation? A downpipe cannot be compared to two operational equipment that do not have the same potential.
 

Similar topics
28.02.2013Heat demand calculation according to DIN 1283112
24.03.2014Heating proof: Heat load calculation according to DIN 12831 or DIN 4708?10
10.09.2015DIN 4109 Noise - What is to be considered?13
28.11.2016Is sound insulation according to DIN standard 4109 relevant for building permits?16
02.06.2016Sat multiswitch in the attic or basement?22
09.11.2018Is installation of surge protection according to DIN VDE 0100-443/543 mandatory?15
15.09.2017Is a lightning rod still needed?25
28.04.2024Potential equalization for satellite must be laid separately17
18.10.2018Construction costs for terraces, etc. in cost estimation according to DIN 2719
26.01.2019Proper grounding in steel fiber concrete and black tank11
17.11.2019Satellite system - buying guide and installation41
20.02.2020What does the electrician do during the shell construction phase?19
14.05.2020Sound insulation VDI Guideline 4100 & DIN 4109 in prefabricated house construction49
24.11.2020Heating load calculation & layout plan DIN: Is a new calculation necessary?41
27.06.2023Is sound insulation according to DIN 4109-1 sufficient for a mid-terrace house?19
15.12.2022Planning guest WC in new construction - How big should it be? (DIN?)107
27.12.2022Door DIN left or right – are both possible?17
07.11.2024Is window planning mandatory according to DIN 5034-2021-08?13
20.11.2024Is staircase DIN 18065 mandatory or not?82
14.02.2025The planner does not perform any calculations according to DIN 27660

Oben