Newly built single-family house, first occupancy in Impflingen

  • Erstellt am 2024-12-30 16:46:26

ypg

2025-02-10 17:35:21
  • #1
Even despite problems with the heat pump, I say: congratulations!
 

jokersmile

2025-02-11 11:01:19
  • #2
I am not familiar with the regulation of Bosch heat pumps, but a few things caught my eye at first glance that have nothing to do with your problem right now, but are not acceptable like this:

- Installation position of the domestic hot water circulation pump is wrong, it won’t last long like this
- Shut-off between drinking water safety valve and storage tank is not permitted (if it is closed and the heat pump heats the storage tank, it can burst)
- Installation position of the drinking water safety valve lying down is not allowed, the discharge pipe is also missing. If the expansion vessel (why anyone still installs such a germ incubator nowadays) is broken, the water will flood your technical room
- Thermal insulation is completely missing
- Whether the Cosmo standing tank is suitable for heat pumps at all due to the small heat exchanger surface should be clarified with a phone call to Bosch Service, I can’t imagine it
- If I see it correctly, the domestic hot water circulation line is connected with a T-piece at the hot water outlet. I lack the imagination of how the pump is supposed to draw the hot water from the storage tank.

If the rest of the system looks the same.
 

jokersmile

2025-02-11 11:09:29
  • #3
- Drain at backwash filter is missing
- Drain at system separator is missing
 

jokersmile

2025-02-11 11:15:56
  • #4
- Air pocket in the return line? from the storage charging line (where the expansion tank nailed to the ceiling is connected). The automatic air vent is positioned lower than the pipe

The longer you look at it, the worse it gets. I can also well imagine that the entire system is not properly vented. The heat pump then doesn’t remove the heat but continues to run due to the minimum run time and eventually shuts off with a relatively high flow temperature.
 

scor3E1990

2025-02-11 11:21:25
  • #5


Thank you very much. We will bring in a master technician to assess the situation and, if necessary, take action against the client.
 

scor3E1990

2025-02-16 12:03:12
  • #6
There is a new update. On Tuesday, the heating engineer is coming to take a look. What do you think about that?
 

Similar topics
25.01.2016Hot water only with heat pump?10
10.10.2017New photovoltaic system with storage in single-family home - experiences39
06.09.2014Siemens or Bosch dishwasher combined with Behälping rail14
24.10.2016Ikea Metod + BEHJÄLPLIG + Bosch Grundstück = Problem22
31.10.2015Install Bosch SMV68M90EU dishwasher in Ikea Metod23
16.10.2017Bosch fridge-freezer combination for Ikea Metod cabinet 60x60x22016
21.09.2016Questions about Bosch SMV GSP in Ikea Metod kitchen unit11
30.01.2017Ikea Metod cabinet for built-in Bosch refrigerator HND22K20011
13.07.2019It takes a long time for hot water to come27
20.11.2019A circulation pump for hot water. Yes or No?41
07.05.2020Collaboration of air-water heat pump, photovoltaic system, and storage38
27.09.2020Oil heating system approximately 25 years old, storage defective15
12.07.2021Simple Smart Home System - HomeKit: Bosch, Opus or others?12
20.08.2021Hot water 60 degrees due to Legionella risk12
09.08.2022Decision for a heat pump29
15.11.2022Tecalor 8.5 Air-Water Heat Pump: Warm water - not hot in the morning21
20.09.2023Convert hot water from solar thermal system to photovoltaic system?12
17.10.2023Evaluation of Photovoltaic System Offer with Storage78

Oben