Dimensions of the base plate do not match

  • Erstellt am 2017-02-18 17:59:57

Bieber0815

2017-02-19 13:15:19
  • #1
I would check DIN 18202 tolerances in building construction to see if it is still within limits.

Example: For a length of 6 to 15 m, a clear dimension in the floor plan may deviate from the target by +/- 24 mm. Phew, that’s going to be tricky ...
 

jamal-01

2017-02-19 14:11:00
  • #2
Just measured again. Exactly from corner to corner it is 24mm too little. When I measure exactly in the middle of the base plate, it is 10mm too little. And the other side from corner to corner it is 5mm.
 

11ant

2017-02-19 21:54:59
  • #3


No, not for a "length," but for a "measuring point distance." The specified tolerance therefore applies to the distance, e.g. if you set the first measuring point at 7.32 m and the second at 22.32 m, for these 15 m in between just as for the 15 m from 3.24 to 18.24 m. The total length can also be 27.11 m.

That means you do not have to start measuring at a corner and accordingly do not have to find a new deviation from the standard table for each total length. Rather, for any section of a maximum of 15 m, the 24 mm must not be exceeded.

Only when the total length is so short that the second measuring point could no longer be found at a distance of 15 m (logically the case with 14.99 m or less total length), do you have to look for the corresponding tolerance for 1 to 5 m.

So firstly, no magic, and secondly (before the original poster asks the same again): yeah yeah, all good!
 

DG

2017-02-19 22:21:55
  • #4


Yes, you have to start at a (measured) corner. The deviation between arbitrary points that have no nominal coordinate is always zero – you can measure 1000 times, nothing will come of it. At best, a calibrated measuring tape.



14.99 > 5m. Therefore, a tolerance class for 1-5 m applies in any case.



Indeed.

Best regards
Dirk Grafe
 

Bieber0815

2017-02-19 23:01:52
  • #5
Do I have to understand the difference?

He measures between two points about 10 m apart. He finds a deviation from the expected value of 24 mm. Are you sure that's okay? Can you explain that? If he measures again and finds a 25 mm deviation, is everything still okay?

BTW, I also measured my base plate at the time, but only determined "10 meters". Not to give the wrong impression here; I didn't write the DIN.
 

Knallkörper

2017-02-19 23:06:51
  • #6
More important than a 25mm tolerance is probably that the base plate is not only a parallelogram but also a rectangle. THAT is what I would check.
 

Similar topics
21.10.2011Floor slab insulation "Yes!" or "No!"14
18.09.2012Construction of a base slab with frost skirt but without foundation10
31.05.2015Wastewater pipe concreted in the floor slab at the wrong location29
14.09.2012House financing - house, garage, and foundation slab approx. 290,000 EUR11
26.10.2012External perimeter insulation floor slab, basement mold risk11
21.11.2013Is the floor slab still possible this year?15
15.07.2014Foundation slab for Danwood bungalow? Company for complete works?11
23.11.2014Stone throw on foundation slab - builder's liability insurance?16
15.06.2015Base slab or strip foundations for garage12
07.09.2015Minimum distance from the base plate?11
11.09.2016Base plate - construction/insulation etc. - experiences please!10
05.08.2016Leave the floor slab over winter15
20.08.2016Base slab vs strip foundation15
13.09.2016Insulation under the floor slab EPS or XPS?12
07.08.2018Full vinyl vs vinyl with HDF board27
21.04.2019Floor plan planning shortly before submitting the building application1420
22.09.2018The floor slab for the sewage pipes was poured incorrectly!10
17.04.2024The wall is not level on the base plate or protrudes by 2 cm26
22.09.2022Basement without additional flooring / cleaning floor slab34
11.07.2024Which garage at what cost?37

Oben