The crucial factor is the planned air volume per outlet (i.e., m³/h per outlet). This allows considerations regarding flow velocities and pressure loss to be made (depending on the pipe used and the type of valve). Low velocities and low pressure loss should be aimed for.
If a good planner is found, "erhöhte Schallschutzanforderungen" could be agreed upon and then let the planner do their work.
In the design case, we have 35 m³/h through a floor outlet in the bedroom, which I do not at all find disturbing. If I could plan completely freely, I would probably aim for no more than 30 m³/h. But—as mentioned above—it depends.
If a good planner is found, "erhöhte Schallschutzanforderungen" could be agreed upon and then let the planner do their work.
In the design case, we have 35 m³/h through a floor outlet in the bedroom, which I do not at all find disturbing. If I could plan completely freely, I would probably aim for no more than 30 m³/h. But—as mentioned above—it depends.