Whom to entrust with the room-wise heating load calculation?

  • Erstellt am 2020-02-02 12:23:02

hegi___

2020-02-03 20:10:22
  • #1
Especially in the case of renovation, particular attention should be paid to the design of the overall system. If you install a heat pump. With only a 5 or 10 grid, it is not enough.
 

annab377

2020-02-03 20:25:13
  • #2


On the topic of Energy Saving Ordinance heating load from the heat pump consumption database de
 

Pinky0301

2020-02-03 21:58:51
  • #3

Why?
 

hegi___

2020-02-04 08:25:54
  • #4



    [*] All circuits should have a low and as similar as possible pressure drop. Accordingly, the largest and smallest circuit must be coordinated.
    [*] The installation distances should be precisely adjusted to the heating load of the room so that the desired temperatures are reached without the need for throttling and regulation. (5 cm makes little sense. You only increase the pressure loss without significant additional performance. See attachment)
    [*] The system should be designed for the lowest possible flow temperature.
    [*] The heat pump should run as continuously as possible and not cycle. Therefore, it should not be oversized.


The efficiency pump alone can consume between 35-90 watts. With 16 hours of runtime per day, this corresponds to between 55 and 140 € per year just in pump electricity cost difference.
Additionally, there are the efficiency losses of the actual heat generation, which can be many times that amount.

Therefore, I would always have the design checked by an external party. The costs simply add up enormously over the operating period.
 

Pinky0301

2020-02-04 08:35:25
  • #5
Oh dear, I see the next topic I still need to read up on... Thanks ! I will ask the energy consultant. Of course, we could also go bigger than 10cm (15cm), but I thought that would be too big anyway. Intermediate steps are unfortunately not possible. That is probably the compromise you have to make with a low build height.
 

guckuck2

2020-02-04 09:02:06
  • #6


My heat pump with 6.1kw, not modulating, has so far run a maximum of 3 heating cycles of 2-3 hours per day this winter. Yes, it has been mild so far, but that’s how it is in theory with continuously running heat pumps and pumps.

Some a***hole even advises against modulating heat pumps for these reasons, because continuously running circulation pumps counteract efficiency.
But these are peanuts and theories.

Outside the heating season, the circulation pump has even less to do, certainly not 16 hours.
And so 55 to 140 € will more likely become 10-30 € optimization potential.
 

Similar topics
20.10.2016Water-bearing fireplace stove floor heating, heat pump, photovoltaic, new construction?28
23.02.2015Air-water heat pump with solar thermal and fireplace? Cost/benefit/meaning34
26.08.2015Cost Breakdown Heat Pump - Heat Pump with Ground Collectors23
19.05.2021Experiences with brine heat pump491
06.12.2015Heat pump / final energy demand / annual performance factor20
21.02.2016Calculate heating load to determine the size of the ground source heat pump24
21.06.2016Heat pump with photovoltaics vs gas and solar thermal52
20.06.2016Gas or Air-Water Heat Pump16
22.05.2017New build bungalow - air-water heat pump, photovoltaic and solar thermal?17
10.04.2018Gas condensing boiler, air-water heat pump, fuel cells - please advise29
15.02.2019Current test reports air-to-water heat pump19
17.09.2020Alternative to Proxon air-to-air heat pump?28
05.02.2020LW Heat Pump Alpha Innotec LWDV with 12KW26
02.04.2020Heating load calculation 10.3 kW, is a 9.5 kW air-to-water heat pump sufficient?29
24.05.2020Heat pump and BAFA - What is true and what is not?24
14.10.2022Air-to-water heat pump sizing in new construction311
05.10.2020Air-to-water heat pump single-family house with basement - 150m² living area19

Oben