In an air-to-air heat exchanger, the heat transfer can theoretically only occur up to the point where the supply and exhaust air have approximately the same temperature, or am I mistaken? That would be the case at 5 degrees Celsius and the parameters mentioned above.
The supply air at the outlet (which is, of course, significantly higher at such low outside temperatures due to further heat uptake within the building envelope) or directly behind the heat exchanger?
Hello.
Here is an excerpt from a manufacturer's product description. The controlled residential ventilation should have approval for passive houses (which I believe most do):
"...To be awarded the Passive House certificate, a demanding testing procedure must be passed. The ventilation unit must achieve a minimum supply air temperature of 16.5°C without additional equipment even at an outside air temperature of -10°C. This is important because passive houses do not require additional heating surfaces on exterior components. Therefore, the supply air temperature must be limited at the lower end to avoid uncomfortable cold air drafts. In addition, the total electrical power consumption of the ventilation unit in operating states intended for passive houses must not exceed 0.45 W/(m³/h) of supplied air volume flow. ..."
Best regards