What flow temperatures are you currently running?

  • Erstellt am 2021-10-24 10:27:23

lesmue79

2021-10-30 15:48:54
  • #1
Taccosetter for the bathroom is already fully open, I have to test the whisper mode, I thought it only reduces the compressor power
 

tomtom79

2021-10-30 15:55:11
  • #2
And the valve fully open as well? The actuator is usually located there.
 

lesmue79

2021-10-30 17:37:55
  • #3
Yes, the valves are open... turning whisper mode on or off has no effect on the pump performance or flow rate in the underfloor heating circuit.
 

Alessandro

2021-11-01 08:41:12
  • #4
what does your hydraulics look like?

the design is such that the specification for 35°C supply temperature on NAT is already being met.
unfortunately, this also means that in most cases "only" 20°C room temperature is taken as the target value.
the bathroom is therefore undervalued for a temperature of 22-24°C. you won't achieve that even if you increase the flow rate.
the only solution here is to increase the supply temperature...
 

OWLer

2021-11-01 08:52:55
  • #5


I have something similar under the actuator, but not a hexagon, rather the "radiator square" for the thing under the pin for the actuator. If I unscrew it, will the flow then increase, or is it simply an adjustment of the actuator’s travel stop?

With my valve, I turned the one on the return line, but didn’t notice any change in flow.

Put differently, what do you have to turn to remove the restriction?
 

lesmue79

2021-11-01 09:06:46
  • #6
Yes, that may be true that I can only achieve the temperature increase in the bathroom with higher flow temperatures. Then the question is whether I raise the flow temperature to achieve, for example, 22°C in the bathroom (which would then apply to all heating circuits) or if I hang up a purely electric towel radiator and have it heat by timer or on demand... Madame wants something like that anyway to hang towels and dry them faster...
 

Similar topics
14.10.2017Heat pump flow temperature experiences?13
11.10.2021Actuators are open but no flow13
07.03.2022Supply temperature from 40 degrees to 35 degrees "pattern" or not31
19.12.2022TGA planner difficulties, underfloor heating supply temperature + wastewater ventilation124
16.03.2023Lowering the supply temperature in underfloor heating more complex than expected?70

Oben