The children's room is too warm in the new building.

  • Erstellt am 2019-11-01 21:59:22

Joedreck

2019-11-11 19:21:17
  • #1
The heating engineer has once again set up a system following the motto "As long as it gets warm." You are taking the first real step!
 

guckuck2

2019-11-11 19:26:05
  • #2


Gas or heat pump?
 

AD1988

2019-11-11 19:40:56
  • #3

It is a gas heating system.

Now that I am dealing with it, I also feel that everything is set incorrectly here. I understand that the maximum supply temperature is set to 35 degrees and would leave it that way. But I have now seen that the minimum temperature is set to 25 degrees. Does that make sense?

I have just seen that at 0.4 and an outside temperature of 5 degrees, the supply temperature should be around 30 degrees. At the moment, it is already at 26 and the heating is still off.
 

guckuck2

2019-11-11 20:14:21
  • #4


Yes, please leave it like that. It is conceivable that the heating-up program only ran up to 35 degrees or slightly above. If now 50 degrees flow into the underfloor heating, it can cause stresses.
(Although so far one can assume that the heating engineer properly brought the system up to temperature during the function heating )



No idea. Could be, depending on other settings. I don’t know Vaillant. Maybe someone else with Vaillant and the same controller will chime in. Otherwise, ask in the pink forum.

Doesn’t sound entirely wrong though. You start with 25 degrees flow, energy is released to the room, and it returns at 20 degrees (5K spread). That’s about right to have any warming effect in the room at all. With 20 degrees flow, you won’t further heat a room that is already 20 degrees warm.



Yes, it should be just above 30 degrees flow. Is a hysteresis set?
 

AD1988

2019-11-11 20:30:22
  • #5


If I knew what that was, then I could check it.
 

AD1988

2019-11-12 12:28:18
  • #6
So the first night is over with the new heating curve and everything is nicely warm except for the floor. But this is okay. Yesterday I found the calculations for the circuits. However, I now know how to properly set the flow rate. Is only the affected circuit opened or all of them? I noticed that the flow rate varies depending on how many circuits are open.
 

Similar topics
26.08.2015Cost Breakdown Heat Pump - Heat Pump with Ground Collectors23
29.08.2016Room Thermostats Heating/Cooling36
13.02.2019Setting gas condensing boiler Junkers Cerapurmodul ZBS 1423
14.10.2022Air-to-water heat pump sizing in new construction311
08.05.2021New construction - floor heating unevenly hot (Vaillant aurocompact)12
09.11.2021Cost maintenance Vaillant Therm plus VWL 75/6 A Height ok?20
30.11.2022Controlled Residential Ventilation & Heat Pump: Viessmann vs. Vaillant vs. Zehnder?47
16.03.2023Lowering the supply temperature in underfloor heating more complex than expected?70
11.08.2023Purchase advice, heat pump comparison: Daikin or Vaillant?19

Oben