The children's room is too warm in the new building.

  • Erstellt am 2019-11-01 21:59:22

boxandroof

2019-11-11 12:05:35
  • #1

That shows that the heating curve is too high. Therefore, that was a good hint:

 

Mycraft

2019-11-11 13:52:44
  • #2
With the correct setting of the heating, the wheat is separated from the chaff.

Companies that cannot handle this have either neglected to continue their education or are simply "plumbers" without understanding what they are doing.

For me, the floors only start to get slightly warm when there are sub-zero temperatures outside. At the moment, everything is cold. Nevertheless, the set temperatures are reached everywhere.
 

AD1988

2019-11-11 13:59:51
  • #3
That's where I want to go too. I have already started reading up and trying to understand the whole systematics. Now I at least know how to calculate the heating load to determine which flow rate I need for the individual rooms. Now the question would be how to set the whole thing correctly.

As far as I have seen, the flow rate changes with us depending on how many rooms are heated at the same time. How do you then set it correctly if the value always varies anyway?
 

Joedreck

2019-11-11 14:07:54
  • #4
So you do the following first: you check how to set the heating curve on your system. Then you open all valves etc. fully. Wait 24 hours. If it is too warm everywhere, you lower the heating curve. You do this until one room is no longer warm enough. Then we'll see further.

You don't calculate anything here anymore. You balance thermally. There are a ton of instructions for this that only require some understanding and patience.
 

AD1988

2019-11-11 17:22:24
  • #5
I just looked at our Vaillant heating system and saw that the heating curve is set to 1.1. Isn't that a bit too high? According to the chart, the water should be heated to 40 degrees at the current outside temperature. However, it is capped at a maximum of 35 degrees. Edit:// I have now seen that the water temperature has been limited to 35 degrees.
 

boxandroof

2019-11-11 17:34:09
  • #6
40 or 35° is too high. In the worst case, you should need 35° flow temperature when it is really cold. The underfloor heating circuits need flow for this: keep thermostats permanently open. Lower the heating curve until it is no longer too warm, then adjust the circuits. Take your time and don’t change too much at once. Notes help. I cannot contribute anything to the setting on Vaillant.

Example of a heating curve in a new building: 24° flow temperature at 10° outside temperature, 30° flow temperature at -14°.
 

Similar topics
21.01.2016Is the heating oversized?44
13.02.2019Setting gas condensing boiler Junkers Cerapurmodul ZBS 1423
02.01.2022Hydraulic balancing air-water heat pump + efficiency circulation pump109
08.05.2021New construction - floor heating unevenly hot (Vaillant aurocompact)12
09.11.2021Cost maintenance Vaillant Therm plus VWL 75/6 A Height ok?20
23.12.2021What flow temperatures are you currently running?192
30.11.2022Controlled Residential Ventilation & Heat Pump: Viessmann vs. Vaillant vs. Zehnder?47
11.08.2023Purchase advice, heat pump comparison: Daikin or Vaillant?19

Oben