Split the underground cable into 2 circuits

  • Erstellt am 2020-03-16 10:37:50

WingVII

2020-03-16 21:21:54
  • #1
The calculation is unfortunately also wrong. With the given values, the voltage drop is twice as high. So 2.66% because the return path is not considered.
 

Vicky Pedia

2020-03-16 22:01:50
  • #2
Just for the sake of clarity and because it continues: 10mm² is quite a statement! And lots of copper! It is mm²
 

Tassimat

2020-03-16 23:31:39
  • #3
Lighting with LEDs hardly draws any power, that will work even with 100m. But what is connected to the "power supply"? The electric lawn mower with just over 1000W is already critical.
 

Dogma

2020-03-17 07:09:35
  • #4
Finally, I have been waiting for a forum troll like you. If you knew it that precisely, you could have helped instead of whining here. And just for your information, the result is correct because the formula contains 2xl (l=length). Maybe you should have asked what is in the formula before whining. Oh man, people... P.S. Your statement that 100m is correct for three-phase current is unfortunately not correct... because in the formula it is not 2*l but square root(3) or also 1.73*l
 

WingVII

2020-03-17 07:47:25
  • #5

Now calm down. Sorry if I offended you.

Why am I a troll if I point out a wrong result? Unfortunately, electrical installations often do not forgive mistakes.

[ATTACH alt="Voltage drop.png" type="full"]44238[/ATTACH]Look, you only considered the simple length

My statement referred to the cable length. It is obviously clear that the line-to-line factor must be considered here as soon as it is about THREE-phase current.

Yes, it wouldn’t be bad if the OP summarizes exactly what he wants to do again. Then we could help him once more.
 

hampshire

2020-03-17 07:53:01
  • #6
Standard LED lighting on 50m 1.5mm² cable is no problem (of course not an unlimited number...) Well pump on 50m 1.5mm² cable better double-check and recalculate (there are very different models from the "pond whirl" to the "C-pipe supplier"). Stronger consumers close to the house to use short cables

Fuses must be correctly sized! You can plan a small sub-distribution adapted to the usage at the point where the cables split.
 

Similar topics
16.07.2015Cable for outdoor lamp too short11
01.01.2016Cost of house connection for Kabel Deutschland and Telekom?37
14.01.2018Kabel Deutschland or Telekom or both14
09.06.2017Computer cables and Wi-Fi router43
12.12.2017Many colorful cables for lamp connection - How to connect the lamp?11
08.04.2021Building without antenna and SAT-CAT cable without conduit?65
01.09.2020Which conduit for LAN cable?32
18.09.2020CAT cable in the utility room - not crimped?45
19.02.2021Telekom Hybrid or Vodafone Cable - Advantages & Disadvantages for Internet36
08.05.2021Connecting LED ceiling lamp - several cables hanging from the ceiling27
28.08.2021Looking for a suitable doorbell for CAT 7 cable12
11.09.2021Which Cat cables should be installed on the facade? Problems with moisture?29
21.02.2022Electric gate, bell and opener, and only one cable33
29.10.2022Is the property fully developed? - Cable is partially missing10
20.09.20225-pin cable to 3-pin cable13

Oben