Hello

The 5-core cable provides 2 circuits. I would distribute them outside onto an empty junction box. One with brown, blue, and green/yellow; the second with black, gray (blue), and green/yellow. If you take the black, brown, and gray as phase (P) and return on blue (N), the blue can quickly overheat.
Maybe you can install a sub-distribution board outside. That way you save the wiring path inside the house.

Steven
 

Knöpfchen

2020-03-18 23:37:00
  • #2
With very long cable runs, not only the voltage drop must be taken into account but also the disconnection conditions in case of a short circuit. If the fuse trips too late, there is a risk of fire. If the cable (insulation scorched, damaged) is affected, impermissible touch voltages can occur. A preceding RCD may also trip too late at these lengths. Therefore, the loop resistance must definitely be measured. Electricity makes you small and ugly.
 