So I'll write down everything I could read from the ServiceInfo:
1/16 Status EB100
Priority control: Cooling
Domestic hot water preparation BT6: 47.1 °C
Domestic hot water top BT7: 51.4 °C
Calculated flow temperature: 20 °C
Degree minutes: 0
Outside temperature BT1: 30.2 °C
Coolant in BT10: 17.1 °C
Coolant out BT11): 19.7 °C
2/16 Climate control system 1 EB100
Flow temperature 1 BT2: 20.3 °C
Return temperature 1 BT3: 22.3 °C
Calculated flow temperature 1: 20 °C
Room temperature BT50: -
External flow temperature BT25: -
Degree minutes 0
External adjustment: No
Floor drying: off
3/16 EB100
Average outside temperature: 27.7 °C
Hot gas BT14: 47.6 °C
Liquid line BT15: 19.6 °C
Suction gas BT17: 35.7 °C
Coolant out BT11: 19.7 °C
Condensate flow BT12 19.5 °C
Flow temperature BT2: 20.3 °C
Return temperature BT3: 22.3 °C
4/16 EB100
Pump speed heat carrier GP1: 100%
Speed of WQ pump GP2: 75%
5/16 EB100
Status internal ZH: blocked
Max. set current flow: 2 kW
Fuse size: 25A
Current L1: 0 A
Current L2: 0 A
Current L3: 0 A
Degree minutes: 0
6/16 Time control EB100
Domestic hot water: off
Heating: off
Cooling: off
Ventilation: active
Schema blocking: off
Holiday setting: off
SG Ready: not used
7/16 Soft inputs/outputs EB100-AA3
AUX1: Tarif blocking (0)
AUX2: not used
AUX3: not used
AUX4: not used
AUX5: not used
X7: DW circulation (0)
8/16 Heat meter BF1 EB100
Heating, compressor only: 28,642 kWh
DHW, compressor only: 7,045 kWh
Heat, incl. int. auxiliary heating: 45,637 kWh
DHW, incl. int. auxiliary heating: 7,873 kWh
BF1: 18.4 l/min
9/16 Integrated passive cooling EQ1
External blocking: No
Calculated flow temperature: 20.0 °C
Cooling/heating sensor BT74: - °C
10/16 FLM AZ1
FLM pump: off
Collector in BT26: 16.4 °C
Collector out BT27: 19.3 °C
Exhaust air BT20: 26.9 °C
Outside air BT21: 18.8 °C
Cooling: off
Version: 9
11/16 FLM AZ2
FLM pump: off
Collector in BT26: 22.3 °C
Collector out BT27: 26.2 °C
Exhaust air BT20: 27.3 °C
Outside air BT21: 26.1 °C
Cooling: off
Version: 9
15/6 Config EB100
Compressor: Bristol 10 kW
Inc. power: 3x 400V
Int. add: 7/9 kW
Heat med. pump: Grundfos UPM2 25-70
Brine pump: Grundfos UPMXL Geo 25-105
Flow sensor: Huba DN20
El. anode: Magnotex
Display type: 0
COMPRESSOR INFO
Master
Status: off
Number of starts: 11,710
Total operating time: 3,353 h
- thereof domestic hot water: 908 h
AUXILIARY HEATING INFO
Status: blocked
Time factor: 2,243
- thereof domestic hot water: 105.9
PRIORITY CONTROL:
Domestic hot water: 30 min
Heating: 30 min
DEGREE MINUTE SETTING:
Current value: 0 GM
Compressor start: -80 GM
Start difference auxiliary heating: 100 GM
Difference between AH stages: 50 GM
MAX DIFFERENCE Flow temperature:
Max. difference compressor: 10 °C
Max. difference auxiliary heating: 7 °C
Is anything missing?
Let me know, I'd rather give you everything you need