KFW40(plus) standard multifamily house cannot be achieved

  • Erstellt am 2019-09-01 16:57:00

curverbox

2019-09-02 10:29:06
  • #1
Sorry, that was my mistake, it was 49cm with Rockwool WLG035 8cm air layer. So 17.5+14+6+11.5=49 The calculation showed that if we use PUR insulation, the wall thickness with 17.5+12+11.5=41cm results in a similar U-value.
 

boxandroof

2019-09-02 10:58:32
  • #2
Thank you for the clarification. With mineral wool as core insulation, the air layer can be significantly less than 8 or 6 cm. A wall thickness of 49 cm with 14 cm insulation is unusual and not necessary.

Whether 024 PUR is sensible due to saving 2-3 cm or whether it is even necessary for Kfw 40 must be considered holistically.

The wall must meet a certain requirement. Now you have changed the wall and it is still not sufficient? If it is obviously not known exactly where the problems lie, then it is not productive to work on the wall.
 

Zaba12

2019-09-02 12:32:04
  • #3

Something is wrong with your place (maybe the north side has a lot of window area :-p) or with your energy consultant.
My reference value for an Energy Saving Ordinance 2016 house is 0.37. Minus the 45% by which the building envelope must be better for KfW40, I would be at 0.2035.

What is your reference value?
 

ypg

2019-09-02 13:16:27
  • #4


May I ask why it should be achieved with great effort and gray hair to reach KfW 40 or 40+? I know some tenants... and all of them, without exception, can hardly make use of noisy ventilation systems and/or super insulated walls and/or these only underfloor heating systems. Then the window is tilted open all day and the ventilation is throttled...
 

Zaba12

2019-09-02 13:31:59
  • #5
They first need an instruction :-p
 

curverbox

2019-09-02 13:45:08
  • #6
Every component of the building corresponds in terms of U-value


Annual primary energy demand QP / QP,Anf is: 2.7 Reference Energy Saving Ordinance 41.22 kWh/(m²a)
Transmission heat loss H'T is: 0.192 Reference Energy Saving Ordinance 0.3523 W/(m²K)
 

Similar topics
19.06.2009Evaluation of the KfW 60 House Contract: Credit Check for House12
27.04.2014KFW 70 is not achieved, target values for gas condensing boilers23
25.10.2015Which heating system? Air heat pump / Gas / Geothermal52
19.06.2015Build according to KFW 70 or the Energy Saving Ordinance 201442
15.12.2019Aerated concrete exterior wall vs. Energy Saving Ordinance13
09.07.2015Energy Saving Ordinance Proof vs. Energy Saving Ordinance Proof + KfW-70 Proof13
19.09.2015New construction KFW 70 house and your opinion on our project18
09.05.2016Compliance with the 2016 Energy Saving Ordinance with the following heating14
03.07.2016U-value of windows - differences15
25.06.2016How important is the U-value of interior walls?12
11.02.2017KfW loan in 2017 for a house under the 2016 Energy Saving Ordinance17
27.03.201724 cm Ytong + insulation or 36.5 cm Ytong63
13.04.2017U-value of windows: 1.3 - is an upgrade worth it?16
07.05.2020U-value outer wall 0.26 - is that okay?13
29.12.2020Y-Tong vs Concrete without extra insulation in practice (heating costs)38
01.07.2019KFW 55 - Insulation under the floor slab37
02.02.2020Insulation under the floor slab - Is it sensible? Experiences39
24.07.2019Energy Saving Ordinance 2016 or KFW 55 for bungalow with air-water heat pump & controlled residential ventilation, optional photovoltaic47
29.01.2021Is the 2014 Energy Saving Ordinance a KfW standard?24
16.08.2021Material exterior walls and interior walls (KfW 55 standard)41

Oben