Is an air source heat pump sufficient for a harsh winter in the Black Forest?

  • Erstellt am 2015-12-29 15:16:00

Bauexperte

2015-12-30 21:22:53
  • #1
**Heating capacity and power consumption of the heating element

As a rule, in the small to medium power range, such as for heating single-family homes, an air/water heat pump is designed monoenergetically. This means that from a certain outdoor temperature, an electric heating element supports the heat pump or completely takes over the heating. Thus, air/water heat pumps can be used up to outdoor temperatures of -20 °C.

An air/water heat pump is therefore not designed according to the standard design point (e.g., at a maximum outdoor temperature of -16 °C) but according to the bivalence point (e.g., -5 °C). This reduces the required heating capacity of the air/water heat pump, but also increases the power consumption of the air heat pump due to the electric auxiliary heating. The required power of the heating element results from the difference between the heating demand and the heating capacity of the heat pump at the standard design point.

As a rule, the heating element capacity amounts to around 50 - 60 percent of the necessary heating capacity. Although the power share of the electric heating element is relatively large, the operating share of the heating element is only about 2 - 7 percent of the total annual heating work, since the outdoor temperature falls below the bivalence point on only a few days per year.

**Source: Energy Experts

Rhineland regards
 

Grym

2015-12-30 22:24:14
  • #2
There is up to 8.8 kW heating rod power (but it must be set accordingly, i.e. the heating rod can also be limited or turned off). That should be sufficient for a house of normal size, even at -25 degrees.
 

ErikErdgas

2016-02-10 15:28:20
  • #3
Hello,
Overall, the energy concept should be examined more thoroughly. KFW 55, air source heat pump, and pellet heating – that does not sound like a coherent concept and suggests high investment costs. The basis is the Energy Saving Ordinance proof, a heating load calculation, but also the available budget as well as user behavior. For independent advice, the developer is the wrong contact here. You should get in touch with an energy consultant, e.g., through consumer advice or the DENA offer (Energy Efficiency Experts List).

Best regards, Erik
 

Similar topics
08.01.2013Air heat pump with fireplace, water-bearing stove, hot water heating26
28.02.2012air heat pump, water-based fireplace stove, functioning, underfloor heating?12
25.06.2020Air heat pump or use gas and solar?300
02.09.2013Which heating system for prefab houses: air source heat pump, geothermal, solar, photovoltaic17
06.10.2013Experience reports air heat pump, wood stove, solar system, noises31
26.10.20132-family house KFW70 heating with air heat pump ventilation and exhaust ventilation14
11.02.2015Air heat pump and electricity consumption50
25.10.2015Which heating system? Air heat pump / Gas / Geothermal52
23.10.2015Prefabricated house heating: Gas / Air heat pump / Underfloor heating22
15.02.2016House planning final: heating components, what makes sense - no air heat pump20
29.06.2016Gas or air heat pump experiences?44
24.01.2017Air heat pump vs geothermal energy, new build 400m233
01.03.2017Gas boiler or air heat pump13
10.11.2017Back payment air heat pump disaster, contracting party, electricity supplier11
03.01.2020Electricity consumption of your heat pumps - comparison values?22
08.06.2020Air-to-air heat pump vs air-to-water heat pump vs ring trench collector - differences50
19.10.2024Air-to-air heat pump air conditioning? Comfort character?17

Oben