Is a lightning rod still needed?

  • Erstellt am 2017-08-03 08:21:52

Dipol

2017-09-15 13:13:36
  • #1
Lightning channels can be blown away by winds and storms.

Numerous side strikes registered on towers prove that lightning primarily but not necessarily strikes the highest points and not always the lowest impedance locations.

Preferred strike points are places with a high concentration of field lines, such as especially lightning rods or building corners.

Where lightning protection systems are required by building regulations or recommended after a risk analysis according to IEC 62305-2, it is not sufficient to install only an external lightning protection, commonly referred to as a lightning conductor (= capture and down conductors and grounding system); this must always be installed together with an internal lightning protection (= equipotential bonding and surge protection).

Lightning protection must therefore not only focus on direct strikes and requires an overall concept that takes into account that the sum of indirect overvoltage damages is approximately five times higher than that of direct lightning damages including total losses.

Therefore, after the transition period of DIN VDE 0100-443:2006-10 and DIN VDE 0100-534:2006-10 expires, surge protection will become mandatory even in new buildings without a lightning protection system.
 

Kaspatoo

2017-09-15 13:28:25
  • #2


a requirement for surge protection (!= (external) lightning conductor) also sounds sensible and should already be implemented by every good electrician
 

Similar topics
28.02.2013Heat demand calculation according to DIN 1283112
24.03.2014Heating proof: Heat load calculation according to DIN 12831 or DIN 4708?10
10.09.2015DIN 4109 Noise - What is to be considered?13
28.11.2016Is sound insulation according to DIN standard 4109 relevant for building permits?16
09.11.2018Is installation of surge protection according to DIN VDE 0100-443/543 mandatory?15
04.07.2017Lightning protection at the house, but how?12
18.10.2018Construction costs for terraces, etc. in cost estimation according to DIN 2719
22.07.2019Foundation formwork made of Poroton bricks39
14.05.2020Sound insulation VDI Guideline 4100 & DIN 4109 in prefabricated house construction49
19.06.2020Is an extra circuit / residual current device really necessary for the office?40
24.11.2020Heating load calculation & layout plan DIN: Is a new calculation necessary?41
27.06.2023Is sound insulation according to DIN 4109-1 sufficient for a mid-terrace house?19
21.06.2022Is SAT grounding possible via a 7x2.5mm² cable?12
15.12.2022Planning guest WC in new construction - How big should it be? (DIN?)107
27.12.2022Door DIN left or right – are both possible?17
28.04.2024Is lightning protection necessary for new buildings?11
07.11.2024Is window planning mandatory according to DIN 5034-2021-08?13
20.11.2024Is staircase DIN 18065 mandatory or not?82
14.02.2025The planner does not perform any calculations according to DIN 27660

Oben