Integral device Stibel Eltron LWZ 504 with central supply air

  • Erstellt am 2014-10-19 20:20:41

guckuck2

2019-11-15 08:05:34
  • #1


Base point for what? Flow temperature?

If you set it like this and no slope, I would expect exactly 20 degrees flow temperature, unless other settings completely prevent the start. Was there even a commissioning so that it is clear that the system already takes the outside temperature into account?
 

ares83

2019-11-15 19:31:32
  • #2
I would agree with that, and 20 degrees is a touch too little at these temperatures The values are completely off. Just as a reference: We are working with a base point of 2.0 and a slope of 0.30 on the 504. Did you receive the manual? This is what our heating curve looks like: This is the result of the last 2 years of adjustment. Let's see if we can go a bit lower now.
 

ares83

2019-11-15 19:36:58
  • #3

Otherwise the heating operation would not be active. It kicks in as soon as the heating detects an outside temperature below the hysteresis of the summer operation. So basically the heating wants to heat, but it only does so until the return temperature is 22 degrees, which does not warm a house.
 

blackm88

2019-11-15 19:38:14
  • #4
We have the same model. Our parameters are: Base point 2.0 Room temp HK1 and HK2 always 20 degrees Slope 0.25
 

guckuck2

2019-11-15 19:43:35
  • #5


I just don’t know the control system. For example, I can also set my system to constant temperature (or room temperature control), i.e. a fixed value.

But the system does have a nice display.
 

pagoni2020

2020-11-13 20:42:17
  • #6

One question: Do you use it as controlled residential ventilation AND as an air heater?
Are you still satisfied?
 

Similar topics
07.10.2016Which heating is recommended for KfW 55?58
02.09.2013Which heating system for prefab houses: air source heat pump, geothermal, solar, photovoltaic17
25.07.2014Energy saving regulation without heating10
30.04.2015KFW70 with gas-solar heating65
21.01.2016Is the heating oversized?44
24.06.2016Question about heat demand determination and flow temperature11
25.10.2016Slope at the farm entrance?16
14.10.2017Heat pump flow temperature experiences?13
08.08.2019Is the garage driveway too steep?10
16.10.2020Driveway planning for large sloped property - 25% gradient43
06.04.2021Building on a slope with approximately 30 percent incline41
12.10.2021Driveway slope / height difference20
07.03.2022Supply temperature from 40 degrees to 35 degrees "pattern" or not31
19.12.2022TGA planner difficulties, underfloor heating supply temperature + wastewater ventilation124
16.03.2023Lowering the supply temperature in underfloor heating more complex than expected?70
07.10.2023How to plan heating with a heat pump in new construction?14
07.11.2023Create driveway with 25% incline?23

Oben