Morning
That certainly won't work, as the system's storage tank only has a standby volume of about 120 liters.
Just imagine a rain shower with 36 ltr/min on this 14kW system. The storage tank will be empty after a few minutes.
If mom in the granny flat has just prepared a bath shortly before, you end up showering with cold water.
Ultimately, it comes down to the flow rate of the water heater, and it may indeed be necessary to adjust the output of the heat generator.
Olli