Your approximately 30 m3 in four days corresponds to about 7 liters of heating oil EL per day. Whether that is a lot or a little depends on the building's energy demand.
Well, there are only 7 radiators connected on the ground floor and they are only set to frost protection because it is still a construction site and unoccupied. However, of course, the newly filled service water had to be heated first; in any case, I will definitely monitor the consumption.
The pump in a solar system is located in the return line; installing it in the supply line would damage it due to the high temperatures of a solar system in summer.
True, many thanks for the hint! I thought it was the supply line because it is the right pipe, but for idiots, the mixers have red and blue colors marked... -.- (so right is the return and blue with the pump)
At 999 on the controller, I would guess the sensor.
As the installer already says himself, "if nothing plausible is measured" = sensor defective.
PT 1000 = at 0° C 1000 Ohm, at +10° C about 1040 Ohm, at -10° C 960 Ohm.
As an electrical engineer, you can surely check that yourself.
Both sensors (sensor 1 is on the roof and sensor 2 in the storage tank) are fine. Of course, I have checked them myself again!
Yesterday the new controller finally arrived, directly installed, connected, and behold: sensors 1+2 now also show plausible values! What I don’t understand is why I cannot manually turn on the pump through the controller?! (According to the ESR 31 manual, this should be possible...)
Another question: Can someone tell me what these "mini junction boxes" are called, in which you can place a terminal block where 2+2 wires are clamped? Unfortunately, the heating engineer only installed one such "box" and the remaining connection points are flying terminals... :O
As an electrician, this is of course a thorn in my side!