How can information such as the Energy Saving Ordinance 2016 be accessed?

  • Erstellt am 2016-01-02 17:54:39

D.Gerner

2016-01-08 15:21:42
  • #1
Energy Saving Ordinance 2014 vs Energy Saving Ordinance 2016 - Comparison
Exterior wall

U=0.28 W/(m²K)

U=0.21 W/(m²K)

Wall against earth, floor slab, walls and ceilings to unheated rooms

U=0.35 W/(m²K)

U=0.26 W/(m²K)

Roof, top floor ceiling, walls to knees walls

U=0.20 W/(m²K)

U=0.15 W/(m²K)

Windows, French doors

UW = 1.3 W/(m²K)
Where the glass (g) may have a maximum of 0.6

UW = 0.97 W/(m²K)
Where the glass (g) may have a maximum of 0.5

Roof windows

UW = 1.4 W/(m²K)
Where the glass (g) may have a maximum of 0.6

UW = 1.05 W/(m²K)
Where the glass (g) may have a maximum of 0.5

Exterior doors

U=1.80 W/(m²K)

U=1.35 W/(m²K)
 

Grym

2016-01-08 15:36:47
  • #2
That was just the Energy Saving Ordinance 2016 vs. fantasy values.

The former values are the relevant ones from 2016.
 

wpic

2016-01-08 17:11:39
  • #3
Answer to the initial question: No

The Energy Saving Ordinance is complicated and poorly structured. The capable and experienced specialist planner (architect) can make a preliminary selection of desired building materials and building constructions for the heat-transferring exterior components as well as for the systems technology (heating, ventilation, air conditioning) during the preliminary design/design phase and can orient themselves on the component specifications of the Energy Saving Ordinance.

Ultimately, however, only the thermal protection certificate from the structural engineer together with detailed calculations provides the final statement as to whether the planned building complies with the requirements (reference building). If not, all adjustment options must be improved until the calculated result matches the requirements of the Energy Saving Ordinance and the Renewable Energy Heat Act, possibly also the KfW (in case of funding or financing through the KfW). The selection of materials is also influenced by statics: aerated concrete blocks with a λ-value of 0.07/0.08 may not be used if their compressive strength is insufficient. In that case, the building design may need to be revised (thicker walls, smaller openings, lower edge pressure).
 

D.Gerner

2016-01-08 17:13:51
  • #4
Have the values from Hausbaugrundriss.de Seems to be an error then.
 

Bauexperte

2016-01-08 17:17:19
  • #5
This is not uncommon at I-Net-Info. Rhineland greetings
 

Grym

2016-01-08 19:11:22
  • #6
Energy Saving Ordinance 2014 Annex 1 and then point 1.2

The table there (Table 2) has been valid since January 2014 and is still valid. It does not specify requirements per component, but only overall.

The tightening from 2016 can be found in exactly this point 1.2 in sentence 2. There, reference is made to the reference building; these reference values are valid for the transmission heat loss for the first time since 2016. For the primary energy demand, however, these reference values have been valid since 2014.

The primary energy demand can be favorably influenced by system technology. In the case of TE, I am 99.99% sure that compliance with the transmission heat loss will always lead to compliance with the primary energy demand. He wants a heat pump and controlled residential ventilation. The primary energy factor of electricity is 1.8. A heat pump with an annual performance factor of 3.6 alone achieves an improvement of the primary energy demand by 50 percent, whereas only 25 percent is required (compared to the reference building with gas).
 

Similar topics
06.01.2012Geothermal vs. Air-to-Water Heat Pump12
21.08.2011Which heating system is suitable for our Kfw 70 house without a basement?15
19.06.2015Build according to KFW 70 or the Energy Saving Ordinance 201442
09.07.2015Energy Saving Ordinance Proof vs. Energy Saving Ordinance Proof + KfW-70 Proof13
19.10.2015New energy saving regulation from 2016 -> What to build?30
30.03.20162016 KfW Efficiency House 55 according to reference values (U-values)39
29.01.2016Price difference new construction, KfW 70, KfW 5513
24.02.2016Construction costs to achieve KFW 55 funding29
30.08.2016Construction and Performance Description - Contract including Energy Saving Ordinance 201415
11.02.2017KfW loan in 2017 for a house under the 2016 Energy Saving Ordinance17
16.07.2017Energy Saving Ordinance, KFW55, KFW40 or KFW40 Plus19
24.07.2019Energy Saving Ordinance 2016 or KFW 55 for bungalow with air-water heat pump & controlled residential ventilation, optional photovoltaic47
17.01.2020KfW Efficiency House 40 Heating Heat Demand22
09.09.2019Where is it most worthwhile to exceed the requirements of the Energy Saving Ordinance?14
20.01.2020Build a multi-family house according to the Energy Saving Ordinance or KFW55?29
29.01.2021Is the 2014 Energy Saving Ordinance a KfW standard?24
18.05.2021KfW energy calculation with cooling heat pump22
07.12.2021Is a brine-water heat pump still worthwhile with KfW 40+?34
26.04.2022Air-to-water heat pump without buffer storage | Heating installer refers to building energy law requirement33

Oben